Air pressure in a pressure vessel can rise or fall at up to 2.5kpa/s.The pressure is
sampled every 0.5 seconds.If range of the the pressure indication is 0 to 1500
kPa, what is the max value of the error due to sampling in % of Span
Answers were Sorted based on User's Feedback
Answer / rizwan afzal
Dear
change in pressure can be +2.5kpa/s or -2.5kpa/s. while
sample rate is 0.5 sample per sec and range is 0 to 1500Kpa
so error is
e=0.5s*2.5kpa/s
e=1.25kpa
now to calculate percentage of error
%e=(100*1.25Kpa)/1500kpa
%e= 0.0833%
keep in mind error can be +0.0833% and -0.0833%
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / markwilcon
Any one able to help??
I have error = 0.5s x 2,5kpa/s=1.25 %
Is This Answer Correct ? | 0 Yes | 1 No |
how flame detectors sense the flame.
if i change range of flow transmitter in th field then does it need to change range in dcs?
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process
why does mA signal preferred for signal transmission?
How to do calibration of magnetic flowmeter
HOW TO CALCULATE ACCURACY OF AN INSTRUMENT. WHICH IS COMPITABLE FOR USE.
Why integral control mode call Reset controller?
Explain , how timer based pneumatic control valve will work ?
How does milli volt is created in themocouple?
how to convert bar to mA?
In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?