Generally in which location ( JB or IO card or DCS) the
thermocouple compensation is done.Also where they measure
the atmosphere temp ( for compensation) in JB OR DCS panel?
How they compensating that atmosphere temp? is any circuit
for that ( like in rtd wheatstone bridge)?
Answers were Sorted based on User's Feedback
Actually compensation is done in Transmitter.Transmitter
have one IC which cslculate ambient temperture.
2.If output of thermocouple is mV then compensation is done
in DCS .
In DCS one temperture sensor is connect to Analog
input card .This sensor measure room temperture using this
temperture we can calculate T/C compensation.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / carl_ellis
Cold junction compensation (CJC) is done at the point where
the thermocouple wire or thermocouple extension wire
connects to the thermocouple input, either an I/O card, a
temperature transmitter, or a thermocouple input on a
recorder/controller/indicator/alarm. RTD's do not need
CJC. Thermistors do not need CJC.
The purpose of CJC is to measure the temperature of the
termainal connection block with respect to the freezing
point of water (because that is the 'cold junction' and the
national standard thermocouple tables are referenced to) a
cold junction at the freezing point of water) and add that
value to the temperature value determined by the EMF/mV
output of the thermocouple.
The temperature of the terminal connection block is affected
by ambient, room, or atmospheric temperature but is also
affected by the heat generated by the device's electronics,
other electronics in close proximity, and whatever cooling
the installation provides. Because all of those factors can
vary in temperature, the CJC involves measuring the
tempeature of the (terminal) connections.
Temperature-sensing ICs, thermistors, and RTDs are used for
CJC measurements. Thermocouples cannot be used for CJ
measurement.
So the answer is that the CJ measurement is made at the
thermocouple input, presumably the I/O card or temperature
transmitter, never at a junction box.
The actual temperature calculation, measured T/C EMF plus
CJC, can be done on the I/O card or in the 'system', a PLC,
temperature transmitter, controller, DCS, whatever,
depending on design.
CJ should not measure room temperature or atmospheric
temperature (although some poorly designed thermocouple
devices do so); CJ should measure the terminal temperature
where the thermocouple wires connect to the I/O. A
temperature transmitter measures the CJC in order to do the
calculation for temperature.
There are special techniques for CJC for high accuracy
calibration involving an ice bath, but industrial devices
use integrated CJC.
Tell 'em Carl sent you.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / phani
the cable termination for the thermocouple is thermocouple-JB-temp transmitter-IO cord(DCS),in this cable termination compensation ll be done in JB only.
Is This Answer Correct ? | 3 Yes | 1 No |
what are the programming languages used in dcs
Can all intrinsic safe transmitters are provided with inbuilt zener barriers? why
How to work & calculated output of the Derivative action in pid controller (Explain Derivative controller)
in split range control system we are using two control valves,but we have only one positioner and one feed back link.so how we use this one feed back link for two control valves?
Sir,I am going to sit for IOCL written test exam. recently.Can anyone tell me the name of 'Objective type Question Book on Instrumentation Engineering ' which will help me. Pl. mail to bidyut_71@rediffmail.com / bidyut.saha2008@indiatimes.com / bidyut.saha09@yahoo.in
what is dc moter.
0 Answers Jindal Steel and Power, Lupin,
what is plc communication?
What pressure transmitter.
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
what is Micro-switch and where it is used......?
testing of thermo-couple?
How do you identify an orifice in the pipeline?