Answer / ginoop .k.m
ma (Linear) =(% *
16)/100 +4
example - ma=
(25*16)/100 +4
linear ma of 25%
=400/100 +4
linear ma of 25%=
4+4
linear ma of 25% =
8ma
ma (sq rt) = (sqrt
of %*16)/10 +4
example -
sqrt ma of 25% =
(sqrt
of25*16)/10 + 4
sqrt ma of 25% =
(5*16)/10 +4
sqrt ma of 25% =
8+4
sqrt ma of 25%
=12ma
| Is This Answer Correct ? | 45 Yes | 7 No |
Answer / sampath
Sq.Root { x / 100 } * 16 + 4 = ____ mA
where, x is the % ( percenteage value )
For eg, 25% Sq.Root { 25 / 100 } * 16 + 4 = 12 mA
50% Sq.Root { 50 / 100 } * 16 + 4 = 15.31 mA
75% Sq.Root { 75 / 100 } * 16 + 4 = 17.86 mA
| Is This Answer Correct ? | 51 Yes | 23 No |
Answer / jackass
So, the way you would go about doing square root extraction is by using an analog multipler. An analog multiplier has three inputs Vx, Vy & Vz. The output is given by Vo = (Vx*Vy)/Vz; If we set Vy = 1V and Vo = Vz through a feedback loop, we get Vo.^2 = Vx => Vo = sqrt(Vx).
If the interviewer further asks about an analog multiplier, you could mention that it can be designed by a combination of logarithmic/anti-logarithmic amplifier and an adder.
Hope that helps!
| Is This Answer Correct ? | 2 Yes | 14 No |
I am working in a process industry, in that there are several sections devided in the SCADA screens and individual sections may START independently. But sometimes i am facing problem i.e, if section 2 Stopped by the operator immediately Section 1 or Section 3 or Section 4 is getting stopped can you expain the reason behind this?
During valve sizing from all calculation you got flow coefficient CV 12,than what it means? like for selecting pressure transmitter if your MAWP is 12 bar than you select a capsule of max. 20 bar which cover your mawp 12 in same way for selecting control valve If CV is 12 than how we use it in selecting valve??????
What is the use of the shield wire and how is the connection at both the ends of a shield wire?
What is maintenance planning?
Difference b/w SCADA & DCS
what is the conductivity sensor output formula and what is the ph sensor output formula?
In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter
Advantages of servers over normal desktop in PLC SCADA system
What is the use instrument barriers? Can you give me review materials about this?
What do you do as a Engineering person EPC for Sizing&Selecting Control Valve?
Y to use 4 to 20ma instead of 0-10v
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)