If the neutral wire go pass through the core balance current
transformer? If yes then why? and no then why?
Answers were Sorted based on User's Feedback
The neutral is requiered to pass through the core balance
CT together with the phase for the same circuit. It
operates on the current going through the pahse being
balanced with the current returning through the neutral. If
these are balanced the protection will not operate. If a
fault occurs (a short circuit to earth in either the phase
or neutral)some current will flow through the earth to the
neutral and not go through the CBCT. This will then operate
the protection.
Is This Answer Correct ? | 6 Yes | 1 No |
If Current Flowing through the cable is balanced then
output of the CBCT through which the cable is passing is
zero. If you pass the Neutral through the CBCT and if fault
occurs then part of fault current will flow through the
Neutral which will also travel through the CBCT and CBCT
will not produce any output hence Protection will not
operate. Hence Neutral should not be passed through the CBCT
Is This Answer Correct ? | 3 Yes | 4 No |
how to caluclate cable size by Amps
If there is volagte between earth and neutral, what should be the reason ? and solution * What should be allowable limit in case, if the voltage between earth and neutral exist ? / OR what is limit for safe voltage between earth and neutral?
What do you mean by reverse current braking of an induction motor?
where AVR is connected in power plant.
7 Answers ABB, Saudi Red Bricks,
what is frequency response?
How i can select current transformer and meters for the upgrading the panal..for 200kw to 600kw....i need to select monitoring and protection ct,s and apmpire meter ,kw meter too.
How do you find HT and LT sides of a distribution transformer only by looking at it from outside?
How can we save electrical cost i.e switchgear, wiring, conduiting etc in a room?
Define reserve-generating capacity?
How grounding is different than earthings?
why do we prefer a 3-phase delta connected load rather than star connected?
WHAT IS FAULT CAPACITY OF HT MOTOR TERMINAL BLOCK? ANY BODY HAVE ANSWER PLZ....POST IT.