what happen "when Dyn11 is parallel operation with Dyn1"?
Answers were Sorted based on User's Feedback
Answer / akhilesh singh
Due to 60deg phasor diff., PD of two secondaries will
arise. Therefor a circulating current between these two
secondary flows which causes shortcircuiting.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dubai
I agree with murali.
Transformer having -30˚ angle (here DYn 11) can be
paralleled with +30˚ (here DYn 1) angle by reversing the
phase sequence of both primary & secondary terminals of one
of the transformers eliminating phase angle errors.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / thatharao
Both the terminals will reverse and Phase displacement will
be zero.So phase angle will be zero.
Is This Answer Correct ? | 1 Yes | 0 No |
here phase difference between to secondaries will be 60deg
transformers belonging to dy1 could be operated in parallel
with those of dy11 or viceversa by transposing two of
external high voltage connections of one of the
transformers and also corresponding low voltage external
connections .it is not necessary to change any internal
connections
Is This Answer Correct ? | 9 Yes | 13 No |
Answer / ramniveth and subuhani
same pottential of two neutral cannot be earthed .because
it give rise to third harmonics.so it cannot be paralleled
Is This Answer Correct ? | 7 Yes | 11 No |
How to calcute the cable size for both HT and LT please specify the formula for that Regards Chethan C
WHY IL=IPH IN STAR AND WHY IPH=IL/1.732 IN DELTA? WHAT IS REASON BEHIND IT?
can we use IGBT as a AC-DC converting device in the applications?
Why the Potential transformer Primary in connected to Earth?
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts same result on 24Volts and with ground 12Volts only expert answer that thanks we can not ground the battery.
what is the difference between isolator and circuit breaker
No load test of induction motor is carried out to compute= A stator resistance B rotor resistance C magnetizing reactance D rotor reactance
I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions
will 1050kva DG set withstand for back charge of 16MVA transformer
how can you calculate the value of external resistance inserted in a slipring industion motor? (eg. 110 kw / 990 rpm/50Hz/stator v-415/stator Amp-195/Rotor V-440/Rotor amps- 151.)
what is the major difference between LIBBP & HIBBP.. which one is most preferable..
compressor compresses air means exactly what happens?