what happen "when Dyn11 is parallel operation with Dyn1"?
Answers were Sorted based on User's Feedback
Answer / akhilesh singh
Due to 60deg phasor diff., PD of two secondaries will
arise. Therefor a circulating current between these two
secondary flows which causes shortcircuiting.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dubai
I agree with murali.
Transformer having -30˚ angle (here DYn 11) can be
paralleled with +30˚ (here DYn 1) angle by reversing the
phase sequence of both primary & secondary terminals of one
of the transformers eliminating phase angle errors.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / thatharao
Both the terminals will reverse and Phase displacement will
be zero.So phase angle will be zero.
| Is This Answer Correct ? | 1 Yes | 0 No |
here phase difference between to secondaries will be 60deg
transformers belonging to dy1 could be operated in parallel
with those of dy11 or viceversa by transposing two of
external high voltage connections of one of the
transformers and also corresponding low voltage external
connections .it is not necessary to change any internal
connections
| Is This Answer Correct ? | 9 Yes | 13 No |
Answer / ramniveth and subuhani
same pottential of two neutral cannot be earthed .because
it give rise to third harmonics.so it cannot be paralleled
| Is This Answer Correct ? | 7 Yes | 11 No |
Why Transformer does not work in DC ?
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
BSNL TTA EXAM QUESTION
If 11 KV breaker on the primary side of a 11 KV/3.3 KV 12.5 MVA transformer can be installed at a distance of 1000 mtrs through a 11 KV cable. If no what are the probable reasons.
what is the main function of contactor?????
Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer
how to calulate bearing number of any motor ?
On what basis do you decide the ONAN (Oil Natural air natural) or Dry type transformer for a project?
In order that work may be done:(a) Two wires are necessary(b) The circuit must have a switch(c) Coal must be burnt(d) A supply of energy is required
How transformer neutralshould earthed ? Transformer neutral connected to earth mat in substations, right or wrong ?
what is mean by flux
what is the ATS .And how it works.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)