How can one improve linearity of an RTD based temperature
measurement system?
Answers were Sorted based on User's Feedback
Answer / guest
RTD has +/- 0.4% nonlinearity when used over 0 to 200 degC.
This is due to the relationship R= R0*(1+aT+bT^2). The
change in resistance for 0 to 100 degC is 38.5ohms for a
Pt100, while it is lesser at 37.3 ohms fro 100 to 200 degC.
Using a two slope method, one for 0 to 100 deg and another
for 100 to 200 degC, the linearity error can be brought
down from +/- 4% to +/- 0.1%.
| Is This Answer Correct ? | 5 Yes | 3 No |
How can I read the electrical drawing easily?
Why using negative voltage in vibration measurement?
1 How to calculate dp transmitter steam and water? 2 impulse line for liquid steam and gas
1 Answers Sitara Chemical Industries,
Name some of the common protocol use in automation.
on interface level transmitter model(RTG3302-EMERSON) What is threshold valve how can we select correct threshold value T1,T2,T3,T4 When interface water & hydro carbon
What is the absolute temperature
what is field bus system. need defination
How to Calibrate Flow Switch in field
Why we are using sqare root in flow?
What is megering????
WHY RESISTANCE TEMPERATURE DETECTOR IS AN ACTIVE DEVICE
Why do we use triad cable for RTD to Temp.transmitter connection? Why we don't use 3 core cable?
1 Answers Process Control Technologies,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)