Answer / guest
RTD has +/- 0.4% nonlinearity when used over 0 to 200 degC.
This is due to the relationship R= R0*(1+aT+bT^2). The
change in resistance for 0 to 100 degC is 38.5ohms for a
Pt100, while it is lesser at 37.3 ohms fro 100 to 200 degC.
Using a two slope method, one for 0 to 100 deg and another
for 100 to 200 degC, the linearity error can be brought
down from +/- 4% to +/- 0.1%.
| Is This Answer Correct ? | 5 Yes | 3 No |
What is mean by Adapter block and net block?
What is a snubber circuit?
What are de-saturators?
If you SOURCE your outputs from a PLC, would you have to make the output HIGH, or LOW, in order to switch an output ON?
how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?
what are the following documents comes under loopchecking
in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.
how do we commission inergen system?
What does a fire detector detects?
What is the constant voltage unit?
Can be operate control valve without positioning if yes ? how and why?
Q- What are the application in which PNP transistor is preferred over NPN ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)