how to set calibration range in a DP transmitter to measure
level for a closed tank and for an open tank,and also please
explain me how to set calibration range for a DP flow
transmitter in a line ?
Answer / carl_ellis
Configuring the range for a DP transmitter
Open tank:
- Flanged DP transmitter
- high side at lower flange
- no remote seals:
- units: water column units = uwc
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
Closed tank:
- flanged DP transmitter
- high side at lower flange
- no remote seals
- dry leg from vapor space above liquid is piped/connected
to the low side
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
When the receiver (DCS/PLC/indicator/recorder) receives the
level signal, it converts to physical level elevation by
dividing the process level signal by the specific gravity
and scaling to physical level units.
Volumetric flow rate with DP transmitter on DP flow element:
- units: water column units = uwc
- LRV = 0.00
- URV = maximum DP value at the maximum flow rate stated
on the sizing sheet of the DP flow element
Whether the signal is square rooted in the transmitter or
in the receiver for conversion to flow rate is up to the
plant convention/standards.
| Is This Answer Correct ? | 2 Yes | 5 No |
what is the equation for gas flowmetering? whic includes gas flow, pressure, and temperature.
Anybody can tell me how to convert mmHg2o /psi to scfm please give me formula of conversion
Reasons for using seal pots:
What is the full form of PMMC ?
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
difference between plc and dcs?
How to measure the dust in chimney(spm)?
how does we calibrate a square root flow transmitter ,give an example and explain it step by step like range calculation , calibration hook up series connection , zero check , and how to apply pressure , and if not geting proportional output then what should we do ?
pls give me presant awerness quistion and answer in my emailid.
why the supply frequency used in America is 60Hz while that used in India is 50Hz?,
how to solve temperature error in compressor?
What is the difference between fiber optic cable & Ethernet cable
2 Answers BEMCO, CCC, Pidilite,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)