When a field input to plc is coming from 400 to 600 meters
and the input is in 24 V DC? So signal cable of which cross
section i should select for proper signal to plc?
Answers were Sorted based on User's Feedback
you can use 0.5 Sq mm shieled for analog .....Upto 600 m no
problem ....but generally as per standerds above 500m you
will have to go with Fibre optic cable
Is This Answer Correct ? | 9 Yes | 6 No |
Answer / laxit
For this type of circuit, use Relay output instead of
direct driving through the PLC output. As these SOV's are
not the low power wattage, Prefer to use 2.5 Sq.mm as a
general for such digital output.Relay contact shall be
selected accordingly.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jayeshpateler
as per the 1cm3 core wire will be find also check the
current require then as per the current if it is higher
than you can carry but if current is low then you need to
use the repeater for that.
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / mwah
yes gaurav kale is right about 0.5 sq.mm twisted pair
shielded cable but u have to install repeater to make sure
theres no degrading of the signal at the end.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / janes
It is all depends on the Load of the Field Instrument.
After Getting the load apply the Voltahe Drop Formula.
Also the input is 24VDC but define the Amp. is it 20A/ 10A.
that is 24Vdc 10A.
For 24VDC 10A Power supply and the Field Instrument is SOV
with 18 Watts, and the Distance is 600 meter then use the 2
Core 2.5 Sqmm Cable as per below Formula.
% Voltage Drop = Length X Current X R Cos0 + X sign0 /
Number of run X Voltage X 10.
Is This Answer Correct ? | 2 Yes | 5 No |
How to Calibrate Temperature Switch in field
What's the Installtion procedure of DP Transmitter for Gas,steam and water?
how to define range of dp level xmeter in open tank
what is compensation in engineering and what is temperature compensation?
I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea
Why went
How to convert milliampares into flow??
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
What is pressure,What is temperature,What is flow,What is level
What is an antisurge control system, how it works?
why t/c is connected parallel and what is the purpose of it
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.