Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is the Difference between E/P Positioner and I/P
positioner in a control valve? In which applications the
respective positioners are used in?

Answers were Sorted based on User's Feedback



What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / vishal

I/p convertors converts a current input signal for eg. 4-20
ma to pneumatic siganl which controls the opening and
closing of a control valve and e/p have simmiliar
operations as those of i/p but it can be either a voltage
input based or current input based.

Is This Answer Correct ?    56 Yes 11 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / william z butryn

An I/P convertor is a device that converts an electronic
input signal (typically 4-20 MA @ 24 VDC) to a pneumatic
output signal(usually 3-15 or 6-30 PSI) depending on the
control pressure required. The output must be calibrated to
provide the desired percentage of span as the input span.
The output of this convertor will do NOTHING until it is
connected to another device. The other device can be an
actuator, positioner or other device requiring a pneumatic
control signal.

If an actuator is used, the actuator can be connected to a
valve stem, a damper or a lever. The actuator can then be
used to set the position of the connected device by moving
a shaft up and down corresponding to the pressure applied
by the output of the I/P convertor. An E/P can be construed
to mean a device that converts a voltage or electronic
input signal to a pnematic output signal. A P/I convertor
does the reverse and converts a pneumatic input signal to
an electrical or electronic output signal.

An EPP as it really should be designated, is an electro-
pneumatic positioner (which can also be a smart positioner)
that can provide a position feedback to itself through the
use of a lever connected between the positioner and the
controlled device that will move proportionately up or down
with the shaft movement of the control valve, lever or
damper to which it is connected. When the position feedback
signal has reached the corresponding percentage of span of
travel, the output signal will be adjusted accordingly and
stabilized to maintains and hold the desired position of
the device.

Is This Answer Correct ?    46 Yes 4 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / dipak

Basically both are same. Here letter I stands for Current &
E stands for Electric signal which is nothing but current
signal to operate control valve. It's all depends on
legends we are going to use in a particuler project.

Is This Answer Correct ?    38 Yes 28 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / abhinendra singh bhadauriya

i/p is a converter that converts 4-20 ma input signal to an
pneumatic signal(3-15 psig or 6-30 psig).i/p converter took
the input in the form of current (ma)and produce an output
in the form of pneumatic signal (air)which is used to
maitain the position of control valve.
but e/p positioner is an device which also reside i/p
converter inside it along with the positioner , means e/p
positioner is the combination of i/p converter and
positioner which receive the electric signal (as current or
voltage)and convert it in pneumatic form which is
responsible for the operation of control valve.
thangs

Is This Answer Correct ?    8 Yes 5 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / anmol upadhyay

I/p converter is current to pressure that converts an 4-20ma input signal to give output as pressure(3-15)psi.Depending on output of a positioner control valve works.

Is This Answer Correct ?    0 Yes 0 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / senthil

I/P is Current to Pressure converter . Its convert 4 - 20
mA to 3 -15 Psi, This 3-15 psi is not sufficient to operate
valve actuator, so its required additional pneumatic
positioner to operate valve

E/P is current to pressure converter with positioner , its
conert 4-20mA to Pressure (ex: 0 to 3 bar, 1 to 5 bar....),
output pressure of E/P can be adjustable , it not required
additional positioner

Is This Answer Correct ?    4 Yes 5 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / nabeel

I/P transducer or positioner functions for "Current(I) to
Pneumatic(P)" signal converter. It converts "4-20mA of
Current signal" to "3-15psig pneumatic signal".
Whereas, E/P positioner functions for "Voltage
(electromotive force = E) to Pneumatic (P)" signal
converter. It converts "1-5V of voltage signal" to "3-
15psig" of pneumatic signal.

Is This Answer Correct ?    2 Yes 4 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / dinesh wanjari

I/P converter convert 4-20 mA input into 3-15 psi pneumatics output where as E/H converter convert electrical signal input into hydraulically pressure output as per design.

Is This Answer Correct ?    0 Yes 2 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / kk verma

As we know all that IP converter works as current to pneumatic converter i.e 4-20 mA to 3-15 psi output, an EP converts the electrical signal to pneumatic for example SOV, solenoids valves are use for the operation of on off valve and use for fast response in action for valves, and the generally in sov electrical signal are use i.e 110 vdc this electrical signal is open the path of sov by actuating
and pneumatic goes to actuator part and valves operates.

Is This Answer Correct ?    0 Yes 2 No

What is the Difference between E/P Positioner and I/P positioner in a control valve? In which appl..

Answer / s vedpathak

Basically both are same & there is no difference at all
between them.Both are used for controlling C valve. 4-20mA
input to the I/P (E/P) converter converts the current
signal to 3-15 psi which either goes directly to CV
actuator or thro positioner with or without booster(1:1 or
1:2).

Is This Answer Correct ?    5 Yes 8 No

Post New Answer

More Instrumentation Interview Questions

how to calculate flow by dp transmitter?

4 Answers  


What is the cascade control

0 Answers  


Difference between dcs and plc including date processing and architecture.

0 Answers  


why need 3 element system in power plant? if it is not there then what l happen?

5 Answers  


To find closed tank level by DP transmitter , how to findout its range.and insomeplace they using range like - 1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit they range for minus and plus.and why?

1 Answers   Kuwait Oil Company,


How to Calibrate Temperature Switch in field

0 Answers  


why we use cascade control and feed foreword control in 3 element control of boiler drum ?what is feed forward and cascade control system ?

0 Answers   Visa Steel,


How to do gas analysers calibration in AUTO and Manually by using zero and span gas?

0 Answers  


In dcs contol valve parameters showing like this Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me

1 Answers  


Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?

0 Answers  


In bimetallic temp. Gauges why does metal strip bend? Why do we use low expansion factor metal and high expansion factor metal in bimetaliv strip?

1 Answers   Process Control Technologies,


please someone tell me what is function of vibration sencer and how many types and how to control viberation.please. my id is jimmykhan077@gmail.com

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)