What is Integral and Derivative control?
Answers were Sorted based on User's Feedback
Answer / jagadeesh
if the error is reduced by increasing or decreasing the
duration then it is known as integral controller and if the
error is redued with respect to the rate then it is known
as derivative controller.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / rizwan
In simple u can say
Proportional----how much controller will open or close
Integral---how long it will keep the same controller opening
Derivative----how fast controller will complete its action
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mohammed emaaduddin
In Integral control, the value of o/p at any given time is the integral of the error over that period of time.
In derivative control, the o/p is proportional to the derivative of the error..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gnv207
The actual error is directly proportional to the integral
value of the error ,that type of control is called as integral
control.
The same manner the derivative control is
The actual error is directly proportional to the derivative
value of the u(t)error ,that type of control is called as
integral control.
| Is This Answer Correct ? | 3 Yes | 8 No |
how to install Differential pressure transmitter in gas line.i need transmitter down side.
What is the basic principle of vibration measurement by BENTLY NEVADA vibration measurement system? and Why it gives the -ve voltage output?
14 Answers Ensol, GNFC, Reliance, Siemens,
I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width
what is difference between DO and DI
Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??
What is DCS and PLC scanning time?
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?
why we use sensing type(NPN)on a vibration monitring system not a (PNP)sensing type
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
What is mean by Adapter block and net block?
why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V
How can you add value to this Industry if offered the job?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)