To identify the creepage distance
* Define the installation category
* Define the degree of pollution expected
*From the nominal voltage and the type of supply system
select the rated voltage from table 00.03 a/b
*From the rated voltage and degree of pollution select
the minimum creepage required in table 00.04
For the dimensioning of the creepage distance the tracking
formation of the insulating material has to be considered.
If not indicated contrary, the CTI value of the insulating
material is <400 and the isolation group
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / deadzg_devil
Creepage Distance. Creepage is the shortest path between two conductive parts (or between a conductive part and the bounding surface of the equipment) measured along the surface of the insulation. A proper and adequate creepage distance protects against tracking, a process that produces a partially conducting path of localized deterioration on the surface of an insulating material as a result of the electric discharges on or close to an insulation surface. The degree of tracking required depends on two major factors: the comparative tracking index (CTI) of the material and the degree of pollution in the environment. Used for electrical insulating materials, the CTI provides a numerical value of the voltage that will cause failure by tracking during standard testing. IEC 112 provides a fuller explanation of tracking and CTI.1 Tracking that damages the insulating material normally occurs because of one or more of the following reasons:
*
Humidity in the atmosphere.
*
Presence of contamination.
*
Corrosive chemicals.
*
Altitude at which equipment is to be operated.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / k.prakashchandra
The above answer is correct. You can take it as the shortest
path between conductive parts including bounding
surface,measured along the surface of the insulation
| Is This Answer Correct ? | 3 Yes | 0 No |
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
Why phase sequence must be same in any ht motor or generator circuit?if phase sequence doesn't same whatever will be affect on circuit?
What will happen if the generator turns in a wrong direction?
difference between shunt coil and tripping coil
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test. why transformer rating in always in KVA ? what ispositive, negative, zero sequence impedence? How ElCB tripping if Neutral touch with ground Why AC & DC capacitor are use in UPS ? why motor rating in KW? how to syncronize two dg sets
For high frequency application we use which transformer?
What is a feedback in control system?
How dc generators direction can be reversed ??
2 Answers GPSC Gujarat Public Service Commission,
How to connect surge arrester with equipment?
sir i am pradeep singh from electrical branch and i want to place in software industry(tcs)but i dont know much about programmig languages like c c++.so how can i get a placement in software industry?
How to calculate the 2500 Kva Transformer losses Primary 11KV Secondary 415volts
importance of air gap in transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)