This calculation Applicable for 3 phase fault.
Transformer:
Step 1:
First calculate Full load current
I(F.L)=(KVA*1000)/(V*1.732)
Step 2:
Calculate multiplier factor(M)=100/%Z
Step 3:
I(sc)=I(F.L)* M
Motor
Step 4:
F=(1.732*L*I(#phase))/(c*n*E(line-ground))
step 5:
M=(1/(1+F))
step 6:
I(s.c)sym rms=I(s.c)*M
I(s.c) MOTOR=4*I(s.c)
Total fault current =Is.c(trans)+Is.c(Motor)
| Is This Answer Correct ? | 2 Yes | 0 No |
Draw torque - speed curve and load curve of induction motor? mark operating point ?
ow can i get certificate of competency as electrical supervisor and my diploma in electrical engineering from jalgaon.
What do you mean by pf of a generator? Power factor purely depends on the load (wether inductive, reactive or unity) then what does the pf mentioned on the generator nameplate means?
what is the difference between E.L.C.B & R.C.C.B?
Draw a SLD of DG distribution up to main LT panel?
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??
Please give me the formula stating relation between AC & Dc.
resistivity of copper
What current position are you holding in your current company?
What are the factors to be considered during the Synchronization?
Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.
HOW COULD A SINGLE PHASE INDUCTION MOTOR ROTATE IN OPPOSITE DIRECTION???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)