Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How do you select a cable size(Cu&Al) for a particular load

Answers were Sorted based on User's Feedback



How do you select a cable size(Cu&Al) for a particular load..

Answer / ashish

While Calculating The Proper Size Of Cable You Should Know
The Full load current Also You Should Consider The Derating
Factor Of Cable , Cable Current rating varies according to
different types of Cable distribution ie where it above
ground or underground.

Is This Answer Correct ?    51 Yes 8 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / tauseef tarique, engineer(e)

depending upon full load current of the load, the size of
cable is selected. Also calculate the % voltage drop and
see it is in permissible limit or not if is more select the
next highier size of cable.

Is This Answer Correct ?    34 Yes 9 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / panda n.n

Calculate the full load current(10% more).Choose prper
rating of Cu & Al. conductor from the chart.

Is This Answer Correct ?    44 Yes 20 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / abdulsubur

FIRST FIND VOLTAGE DROP THEN FOR THE FORMULA


VD=MV*L*A/1000 WE GET VD
VD =VOLTAGE DROP
L=LENTH OF THE Cable
I =CURRENT IN AMP

Is This Answer Correct ?    21 Yes 4 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / dpl

A cable said to adequately sized when all the following
conditions aer satisfied:
1. Current carrying for steady state operation
2. Short circuit withstand capacity
3. Voltage Drop (steady state as well as during motor
starting)

As cable data provided by manufacturers/standards (ERA
report 69.30 etc) is for certain test conditions, which may
be very different from actual site conditions where the
cable is being installed.

Hence, to obtain the actual current carrying capacity of
the cable during steady state operation of the instalation
coditions of the cable shall be considered and suitable
derating factors (derating factor for group of cables,
Ambient temperature correction factor, derating factor for
thermal resistivity of soil, derating for depth of
installation) shall be multiplied to the manufacturer
supplied data. tehse values could be supplied by the
manufacturer or u can refer standards such as ERA 69.30 or
IEC.

The short circuit withstand level of the cable must be
greater than the energy let through value of the protective
device.
i.e. k2S2 >I2t where,
k = cable core insulation constant (143 for
XLPE)
S = Cable cross sectional area in mm2
I = Prospective fault current, rms in A
t = Disconnection time of protective device (in
seconds)

The voltage drop in A.C. cables shall not be more than 5%
based on the continuous maximum current loading and rated
voltage. During motor starting or re-acceleration the
transient voltage dip at the terminals of any motor will
not exceed 18-20% of the rated equipment voltage.

A cable of length L (km) having a resistance of RC (ohm per
km) and a reactance XC (ohm per km) operating in a three
phase ac system carrying a balanced current I (Amps) with a
power factor of Cos &#934; will develop a voltage drop &#916;V
(Volts):
1. For three phase ac systems
&#916;V = &#8730;3 x I x L x (RC.Cos &#934; + XC.Sin &#934;)
2. During starting of 3 phase motors ( with a starting
current of IST at a power factor of Cos &#934;) the voltage drop
will be:
&#916;V = &#8730;3 x IST x L x (RC.Cos &#934;ST + XC.Sin
&#934;ST)

3. For single phase ac systems:
&#916;V = 2 x I x L x (RC.Cos &#934; + XC.Sin &#934;)
4. For DC systems:
&#916;V = 2 x I x L x RC
The percentage volt drop relative to the rated voltage is
given by:
Vd = (&#916;V x VL) /100 %

Also, one may need to size the cable for earth loop
impedance considerations.

Is This Answer Correct ?    17 Yes 5 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / gulderaiym

Factors like the length of the cable, resistance, current
being carried by the cable , short circuit current, voltage
drop all come into play when selecting cable to be used.

First calculate the load current

I = P / x V x pf
pf =0,9 according to TCO Standard P-ST-2035, point 9.9

Then find apparent power

For three phase: S = x V x I
For single phase: S = V x I

Then I find the resistance by Ohm's law:

Z = V / I
V - is particular Load

Then find the short circuit current

I short circuit = S / Z

Then find cable size

S = I sh.circuit x / k k = 143, t = 1

And then select the cable according to the cable catalogs

Is This Answer Correct ?    3 Yes 0 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / bala

verify motor capacity or kw

Is This Answer Correct ?    7 Yes 5 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / rahul singh

wire size is depend upon the type of wire.
if we used the CU wire then the size of wire should be the 1/5 part of load current and AL wire wire will take around 1/4th of the load current

Is This Answer Correct ?    2 Yes 2 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / salah

Dear Friends,

cable types - XLPE/PVC /SWA

we have to choose the cable depend upon the applied
area/current rating

first step to find voltage drop for a required length as
per IEC regulation the VolDrop should not exceed 4% of
supply voltage it can be calculated

VD= mv/meter/amps this can be get it from cable chart -
supplier .if its ok then we can use

salah

Is This Answer Correct ?    7 Yes 8 No

How do you select a cable size(Cu&Al) for a particular load..

Answer / muralidhara kumar

Generally for copper cable sq.mm2 *2.5
for alluminum cable sq.mm2 *1.5

Is This Answer Correct ?    6 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

Why Ferranti effect is occoured in leading power factor load in a overhead transmission line?

1 Answers  


how does a tube light starter works?

2 Answers  


What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?

1 Answers  


lenz law application and define

0 Answers  


What is the Current equation in series RLC circuits.

0 Answers   ABB, Bhel,


Why used in layer by layer charcoal and salt used in earth pits.

11 Answers   CESC, HP,


Can u explain : how capacitor act when the supply is given is a.c and d.c. I know that when d.c supply is given then the capacitor charges and becomes open circuited. But please say about when a.c is given. I have seen that when a.c supply is given ,it charges and discharges, But when we plug in capacitor to our daily supply and take it out ,then we join those wires spark will appear,which seems charge is present ,but when a.c is given it should charge and discharge

3 Answers  


george phenomenon of synchronous machine

0 Answers   JU,


If we know the load for generator in KW then how it will be change to amps and also if we know the load in amps how it will change in KW and what Generator is good for that...suppose load is 500 amps 3phase......??

1 Answers  


phase colour is indicated by R Y B (red yellow blue) but in transformer i have seen U V W instead of (R Y B) have any meaning of this

3 Answers   Areva, Kim Yew,


How to calculate that clean water supply in one Day from 150 KLD STP?

0 Answers  


what is the difference between star and delta connection ? when we use each one ?what is the best ?

14 Answers   Amara Raja, Daikin,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)