Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is different between Metering CTs and Protection CTs?

Answers were Sorted based on User's Feedback



What is different between Metering CTs and Protection CTs?..

Answer / ramesh kumar k

Mr. RK is partially right.... I will tell you clearly...
CTs are of 3 types depending on their usage... they are
1. Metering 2.Protection & 3. Special Protection(PS)

Metering & Protection CTs name itself self explanatory.

In metering CTs our main aim is to measure the currents
without damaging the instruments (i.e. Ammeters) connected
to it... so at fault levels (i.e. high currents) the
secondary also indicates corresponding heavy currents... so
the meter connected to it will gets damaged... (A 5A
ameeter can't measure 50A)... inorder to make the meter
safe... we will prepare the core of the meter in such a way
that at faults currents the metering CT core gets
saturated... and it will not induce any more current in the
CT secondary... so the current in secondary ckt. is ZERO.
So the meter is safe... THIS METERING CT WILL BE WORKING
WITHIN NORMAL RANGE OF CURRENT AND WILLNOT WORK IN FAULT
CONDITIONS (IT WILL NOT GIVE OUTPUT).

Where as Protection CT will have to work only in fault
condition. Because the line has to be protected in fault
condition only. The core of this CT is made in reverse to
that of metering CT. It will not saturate in fault
condition and still give the output to the relay...

Thats why Metering CT can't be used for protection
purpose... and protection CT can be used for metering but
it will not meet the accuracy requirements (If accuracy
requiremets are compulsory... prot CT can't be used for
metering)


Where as

Is This Answer Correct ?    32 Yes 1 No

What is different between Metering CTs and Protection CTs?..

Answer / rk

metering cts are desined not to record fault current i.e.
if ctr is Ex. 200/5 at a fault current of 2000amp the
secondary current would be still 5 amps not 50amp. reverse
is in prot cts it will serve 50amps if its ALF permits .
Metring CT are like acc class 0.5 etc Protn CTs have 5P10,
5P20etc i.e. it will maintain its ratio up to 20times the
the primary current (200amp)of ct.

Is This Answer Correct ?    13 Yes 4 No

What is different between Metering CTs and Protection CTs?..

Answer / siddharth tayade

mainly the class is diffrence in the protection and
metering c.t.and knee point voltage is conciderd in
protection core

Is This Answer Correct ?    0 Yes 4 No

What is different between Metering CTs and Protection CTs?..

Answer / asit sarkar

Generally CT have two error 1.Phase angle error,2.Ratio error.
Now,in Metering CT we have to minimize the ratio error as
well as in case of Protection CT we have to reduce the phase
angle error.

Is This Answer Correct ?    4 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

What is the diffrece between ACB & MCCB

8 Answers  


why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?

3 Answers   BDL,


wha tis the ac motor used for traction system

4 Answers  


what are the needs of electrical earthing.... other than protection?

5 Answers   Eskom,


What is the latest generation of circuit breakers called?

2 Answers   Focus, Oil India,


The inexpensive way to improving energy efficiency of a motor which operates consistently at below 40% of rated capacity is by _____.

2 Answers   IFFCO, Sanmar,


How can you measure the signal from the PT100 sensor?

1 Answers  


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

0 Answers  


how netral CT is selected (including its details specification)

8 Answers   ABB, ABC, dbpl, Mecon, Shree Engineering, Tapasya Transformers,


why the neutral point of star connnection oscillates?

3 Answers   Avalon,


what is the contact resistance of sf6 circuit breaker??

2 Answers  


Require Generator Capcity ( KVA ) for 3 Phase Motor having 4.7Kw with starting current of 16amps?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)