What is different between Metering CTs and Protection CTs?
Answers were Sorted based on User's Feedback
Answer / ramesh kumar k
Mr. RK is partially right.... I will tell you clearly...
CTs are of 3 types depending on their usage... they are
1. Metering 2.Protection & 3. Special Protection(PS)
Metering & Protection CTs name itself self explanatory.
In metering CTs our main aim is to measure the currents
without damaging the instruments (i.e. Ammeters) connected
to it... so at fault levels (i.e. high currents) the
secondary also indicates corresponding heavy currents... so
the meter connected to it will gets damaged... (A 5A
ameeter can't measure 50A)... inorder to make the meter
safe... we will prepare the core of the meter in such a way
that at faults currents the metering CT core gets
saturated... and it will not induce any more current in the
CT secondary... so the current in secondary ckt. is ZERO.
So the meter is safe... THIS METERING CT WILL BE WORKING
WITHIN NORMAL RANGE OF CURRENT AND WILLNOT WORK IN FAULT
CONDITIONS (IT WILL NOT GIVE OUTPUT).
Where as Protection CT will have to work only in fault
condition. Because the line has to be protected in fault
condition only. The core of this CT is made in reverse to
that of metering CT. It will not saturate in fault
condition and still give the output to the relay...
Thats why Metering CT can't be used for protection
purpose... and protection CT can be used for metering but
it will not meet the accuracy requirements (If accuracy
requiremets are compulsory... prot CT can't be used for
metering)
Where as
Is This Answer Correct ? | 32 Yes | 1 No |
Answer / rk
metering cts are desined not to record fault current i.e.
if ctr is Ex. 200/5 at a fault current of 2000amp the
secondary current would be still 5 amps not 50amp. reverse
is in prot cts it will serve 50amps if its ALF permits .
Metring CT are like acc class 0.5 etc Protn CTs have 5P10,
5P20etc i.e. it will maintain its ratio up to 20times the
the primary current (200amp)of ct.
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / siddharth tayade
mainly the class is diffrence in the protection and
metering c.t.and knee point voltage is conciderd in
protection core
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / asit sarkar
Generally CT have two error 1.Phase angle error,2.Ratio error.
Now,in Metering CT we have to minimize the ratio error as
well as in case of Protection CT we have to reduce the phase
angle error.
Is This Answer Correct ? | 4 Yes | 9 No |
what is meant by re-rolling motor? how it differs from standard motor?
Good morning: I'm looking for some informations about the OLTC or the LTC: I wont to know what the function of the tie-resistor in during the operation of reversing/coarse operation Cordially
how to find the 2500 KVA transformer rated primary and secondary volt and current?
why overload relay is not tripped at time of starting of motor allthough staring current is too high?
What is RMU, and what it's function?
why is the earthing pin on 3 pin top are big and thick
A FIELD MAGNET IS EXITED BY AC/DC?
why does spark appears when we swith on the light
how solar power plant energy meter multiplication factor
Which has more losses, AC or DC??
what are the application of over current relay?
why the substation require din electrical system?