Answer / gaurav tripathi
in the transformer there are two losses,core loss and 'cu'
loss ,core loss depends on voltage and 'cu' loss depends on
current hence rating of transformer is on KVA not on KW
| Is This Answer Correct ? | 22 Yes | 4 No |
Answer / abhishek nigam,akshay kumar si
actually rating of the machine (kva or kw) depends upon the
power factor since the load power factor to which
transformer is supplying power is not known , it may be
capacitive ,inductive , or resistive that is why its rating
is in kva and not in kw
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / manoj
Actually the
rating of a
transformer is
limited by
temperature .here
temperature of a
transformer
increases by
losses that is
core and copper
losses these
losses depends
on the voltare
and current but
almost
indepedent of
power factor .so
it is rated in
kva
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prasanth p.s
copper loss depend on current and core loss depend on voltage
there for total loss depend on voltage and current not on powerfactor .in other equpment like motor total loss depend on
powerfactor ie kw=(v*i*pf)/1000 .there for motor rated in kW.but tranformer rated in kVA because kVA=(v*i)/1000
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / maheshbabu-calicut
the capacity of a transformer depends on the amount of
secondary current,it can deliver safely.(more kw at good pf
and lower at poor pf)
| Is This Answer Correct ? | 0 Yes | 0 No |
what is high tension ? specify the range?
what type circuit breaker is suitable for connecting 1000A load VCb,Mccb?
I have 800 Amps MG Fix type breaker It is in on line & it has been given only UV (under voltage)coil connection for tripping purpose.now it is not working properly means its getting tripp so how can i replace it or how can i rectify the problem without destrubing my load??????????
what should be correct gas pressures to be a 1.5 ac unite
Two electronic energy meters are connected to seperate phase wires, but connected to a looped neutral. Are these going to function correctly?
How can I known multiplying factor .without multiplying table
thermal power station operation in general
11 Answers AJ Square Inc, Jindal, NTPC,
what is function of rtu?
If 110V DC Coil Contactor taken 15ma DC on load,than how much AC current wil be taken?
0 Answers Lafarge, Shree Cement,
why earthing is not required on transformer prymary winding side ???
what is phase voltage and phase current what is line current and line phase
In neutral the current will flow or not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)