what type circuit breaker is suitable for connecting 1000A load VCb,Mccb?
Answers were Sorted based on User's Feedback
Answer / antaratara ghosh
you need to tell the voltage level to know the answer..
If it is HV, you have to go for 1250 A VCB or SF6..
If it is LV, go for 1250 A ACB..
In India, you wont find MCCB of more than 630/800 A..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / chreamz
ABB Sace VD4 17kV, 1250A, 31,5kA MV Circuit Breaker, will
be compatible for this type of Load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / aladdin
hi,
i don't know if there is VCB with 1000A rating !
but in ur case you can use MCCB as it achieve your demands
with low price in comparison with ACB that u can use also.
| Is This Answer Correct ? | 0 Yes | 4 No |
figure of phasor diagram of transformer when full load or no load ?
Why only 1ph,2ph,3ph supplies are universally used?? Why not 4ph or 5ph??
what is the difference between the 94 lockout relay and 86 lock out relay. I have noticed that the 94 lockout relay is activated when the distance realy is activated and 86 is activated when the 87T differential is activated. but why can't the same lockouts be used for both the protection schemes
What happens when ac supply is given as excitation voltage instead of dc supply
when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil
what is GRR(Grid Rotot resistance)?Why it is used beside of LRS?
9 Answers ACC, L&T, Sri Biotech,
If stator & rotor of a 3-phase induction motor have different no. of poles, will the motor run or not??
As we use capacitor bank in 3ph ckt to improve PF, can we use capacitor in single ph domestric use, in house we have Fan,Mixer,electric cooker,iron,tube choke they also lag the system,because it is inductive load. if it is possible to improve PF of single ph system-- if yes- type of capacitor to be used,connection diagram, working in detail. if no-- list it.
What is the dependency of stiffness on load angle??
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?
why link is provided in neutral of an ac circuit and fuse in phase of ac circuit?
A 150KW 440V motor is need to replace in the field instead of faulty one. what are the main parameter should I need to check?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)