the neutral is generated at the secondary side of the t/f,
so the earthing is done at sec. called the dedicated
earthing. but at the pr. side of the t/f no neutral is
generated hence require no earthing. but the body of t/f
is also earthed.
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / jackson
If the primary side of the trasformer is delta, then only
body earth required.delta no eathing is required because
upstream is delta circuit which increase the reliability of
power transmission if earth fault occur. in delta circuit,
no earth fault will be detected.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / t eswara rao
In any type of circuit, the neutral is earthed at source side
In transformer case, the secondary voltage acts as the
source voltage to the load and hence the secondary neutral
conductor is must be earthed.
The secondary currents are transformed in to primary
currents by induction principle. and hence primary side
neutral is not required to be earthed. In other words, the
primary winding acts as load circuit for the partial network.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / shahzad
In case of DELTA/Star Power transformer, the secondry is
solidly earthed because the zero sequance current ciculate
in delta and in star side if ther is no neutral earthed the
protective relay will give false tripping so it is neutral
of secondry is earthed
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / lokeshraj
A power t/f is delta/ star type. Delta side can not be
earthed even there is no need to make in earth as f the
secondary is earthed there will be no or very less fault
current. So the primary will also be safe as no change in
secondary current means no change in primary..
Please post you feedback..
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / dj
Transformer Primary side is Delta Connected, so there we
dont provide Earth fault Protection thats why it is not
solidly earthed, only earthing is provide at transformer
body. But on the secondry side which is usually star
connected, we have to provide solidly earthing to neutral
so that we can use earth fault protection system.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / mahi
HI EVERYBODY, I HAVE A SMALL DOUBT ON THE POWER TRANSFORMER
EARTHING. ACTUALLY THE TRANSFORMER IS DELTA/STAR TYPE, THE
SECONDARY SOLIDLY EARTHED, I HEARD THAT THE PRIMARY SIDE OF
THE TRANSFORMER RESISTIVELY EARTHED. CAN SOMEONE MAKE ME
CLEAR, WHAT RESISTIVELY EARTHING AND HOW IT HAS TO BE
DONE.....???
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / theo
The primary side you don't earth otherwise if you measure on the secondary side there will be no voltage be induce on the secondary side because it will go straight to earth if you provide an earth. there a induction happening between primary and secondary side.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bk
We use earthing for Body Protection.
So there is no meance of Prymary or Secondary.
Between phase we use neutral but for Secondary side
Prymary side Delta connection so we don't use neutral.
| Is This Answer Correct ? | 4 Yes | 4 No |
if we give DC suply to the AC motor what hapen
What is CBCT ? Why & Where it is used?
why exciter frequency 150 Hz ?
I am having 120KVA UPS,which is connected to DG & normal power. What is the power drawn by this system when system is running on DG ????
Weather power factor correction needed for synchronous motors?
Give atleast 20 alternating current apparatus and devices.
TRANAFORMER RATING 500 KVA,33KV/433, SECONDARY SIDE SWITCHED ON ONLY CAPACITOR LOAD 140 AMS, PRIMARY SIDE HOW MUCH VOLTS INCREASE?
1. Can a 12v DC choke operate a 60v/12w PL lamp ? 2. Can a 230v ballast fire / operate a 60v/12w PL lamps.
0 Answers ICS Integrated Computer Solutions,
all the technical question with answers pleas send your email id ramar_eee@yahoo.com
why we use primary delta connectin in hight voltage transformer
How much load can be taken for chiller from 1500 kva transformer
Q-1 what are the structural and operational difference between a distribution and a power transformer? Q-2 what is skew in motors? Q-3 draw equivalent circuit of transformer Q-4 explain with phasors how pf is improved with loading in induction motors Q-5 DIFFERENT METHODS OF CABLE LAYING(interviewer asked if i heard new chemical based earthing system next) Q-6 pi model of medium length trans line Q-7 v/f control?why Q-8 vacuum circuit breaker operates in?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)