Two electronic energy meters are connected to seperate
phase wires, but connected to a looped neutral. Are these
going to function correctly?
Answers were Sorted based on User's Feedback
Answer / dilip kumar
ofcourse both will work satisfactorily ,but if the
connection is used for measurement of 3-phase power then it
will nither give the correct power nor the correct phase
| Is This Answer Correct ? | 4 Yes | 2 No |
yes, if the the 2electronic energy meters are connected
under the same distribution substation it will work, but if
the 2 energy meters are connected in diffrent substation it
will not function properly, becuse neutral only carrying
return current for the single phase loads, if u connect
your elcb getting trip.
| Is This Answer Correct ? | 2 Yes | 1 No |
It is assumed that it amounts to measurement of two phases
of power measurement by two single phase energy meters. Then
the meters will work satisfactorily but sum of two will not
give total power
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / guru
No, when using the electronic energy meters the neutral
should be seperately connected and not a looping.
For example if any fault currents occur in any one of the
phase both the energy will be recorded.
Secondly and main point is electronic energy meters work on
the principle of taking the higher current reading ( Either
it may be in phase or neutral) so if 02 neutrals connected
in loop the sum of the neutral current on both the circuits
will be recorded and the energy value will not be right one.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / raj varpe
yes as the required input is provided to both energy meters
they will work satisfactorily but they are not usable to
measure 3-phase power correctely
| Is This Answer Correct ? | 0 Yes | 1 No |
WhY PF low at Time of PT Missing in HT Meter
what is the need of capacitor in transmission lines?and how it works.
Why are the laminations insulated from each other?
How to improve the power factor from 0.8 to 0.98? Also tell me cost vs benefit analysis.
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
hi if anybody got model questions for cpcl Grade'A' electrical engineer position.send it to my mail please krishkumar22@gmail.com
why we are using the 2 slope in differential relay?but in busbar differential we are using only one slope. what is the reason.
when it is possible kvrah lead & fundamental kwh be equal in electonic trivector meters (3 ph)
What is diversity factor in electric installations?
Refernce currents are to be generated using refernce cueernts how can this be done
how can we solve the RMS value of alternative Qnty is .707 , explain detail .
Whats the type of current and potential transformers?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)