I am working in a process industry, in that there are
several sections devided in the SCADA screens and
individual sections may START independently. But sometimes
i am facing problem i.e, if section 2 Stopped by the
operator immediately Section 1 or Section 3 or Section 4 is
getting stopped can you expain the reason behind this?
Answers were Sorted based on User's Feedback
Answer / chandramauli sinha
There r various possibilities:
1. Its a common stop for all sections and are linked at
single command from SCADA screen.
2. Variable of section-1 is linked directly or indirectly
by process/ logic/ variable to other sections. On stopping
of Section-1, the process/logic of other section is
recognizing as fault and stops the respective sections.
please check that is there any link between these
sections...!
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / chandramauli sinha
There r various possibilities:
1. Its a common stop for all sections and are linked at
single command from SCADA screen.
2. Variable of section-1 is linked directly or indirectly
by process/ logic/ variable to other sections. On stopping
of Section-1, the process/logic of other section is
recognizing as fault and stops the respective sections.
please check that is there any link between these
sections...!
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jigs
It's possible if all sections are in operational interlock. If you stop one then other will be stopped.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jitendra chauhan
following problem may:
1. Is same interlock may used other sections?
2. have you checked stop command DO of all section, may that same DO?
3. may network getting stop, may PLC going to stop while given to stop command?
4. may that same stop command linked on SCADA?
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
this might be due to 2 reasons :
1)scan cycle of the processor has been increased anyhow as
the Dword value is updated after the signal is processed in
module. this extended scan cycle causes difference of
process values on HMI
2) check LAN ports of all stations and also the patch board,
if there is option for redundancy check the healthiness of
redundancy.
| Is This Answer Correct ? | 0 Yes | 1 No |
we want to control pump in let pressure and tank (for exp) our inlet line if water cam and pump will on and when our tank will full pump will off also if our inlet pressure low pump will off even tank not full.this pump i want to uses on our water supply line.
What s the exact height of installed transmitter?
can any one pl explain me in brief that how we select the leakage classification in valve,means for liquid or gas there is any standard for selecting leakage classification or its depend upon valve size or any any other parameter.
What is three element drum level control system why its better than single element?
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
how to use level tranasmitter in closed tank application.?
how to check thermocouple ,its working or not?
14 Answers Coca Cola, Ford, Honeywell,
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
for oil & gas industries which zone is normally preferred? why? give its example?
In bently nevada vibration monitoring system,what is the reason to maintain the Resistance of the probe + extension cable equal to 95 ohm? If possible explain the basic principle of measurement with detail electronic circuits.
what is unit and element of viberation?
To calculate temperature, why we multiply 25 with mV?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)