what is reactive power (MVAR) and how it is control? how it
is generate in powerplant?
Answer / k.prakashchandra
The reactive power on generator can be controlled only if
it is connected to grid/network.If you make the terminal
voltage higher than of grid ,gen will draw inductive power
(lagging pf) and the vice versa.Usually generators are run
at 0.92 to 0.98 lagging pf for system stability.
| Is This Answer Correct ? | 19 Yes | 7 No |
Can anyone explain, How will get positive to ground and negative to ground reference voltage in dc system
how line turns ratio changes in 3 phase with change in connection
How do you connect the capacitors on polyphase circuits?
MCB is used for high rating &MCB is used for lower rating.What is technical difference between ACB & MCB?
what is the potential of 11kv A.B.Switch
I want the details about BHEL company examination.Can anyone able to help me please.
why burdens of VTs is more than CTs?
I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?
Can anyone explain the power flow in flouresent lamps (tube lights) .What are the functions of Starter & choke used there?
How to calculate motor current for 3 ph & 1 Ph motor from KW rating?
What OPGW is better than Microwave or PLCC???
how megger step up the DC voltage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)