How works the AVR in DG Sets Plz explain??????????
The AVR derives its power supply from the line to neutral
terminals of the AC Generator,at a level of 240V AC RMS at
50/60 hz.The sensing voltage,which is regulated voltage is
derived from the line to line terminals of the AC
Generator.The AVR forms an important part of the closed loop
system comprising of the generator field,generator armature
and the AVR.
The AVR,first builds up the generator voltage from its
residual levels to the rated value of 415V.when the
generator is loaded,the sensed voltage goes down and
generates the error voltage,which is required to drive the
closed loop system.The AVR contains a high gain
amplifier,ramp and pedestal circuitry.depending upon the
value of the amplified voltage either high or low the ramp
intersects the amplified volatage at a point which is early
or late in the half cycle.at the intersection point,a firing
pulse is produced to trigger the power device.
When the power device is trigerred early in the half
cycle,more voltage is let into the field and when trigerred
late in the half cycle,less voltage is let into the field.
in order to reduce the generated voltage at lower speed,a
signal inversely proportion to the speed is fed as an extra
input.At higher speeds,the effect is nil while at lower
speeds the voltage reduces more than proportionate with the
speed.
| Is This Answer Correct ? | 5 Yes | 2 No |
What is mean by discrimination of circuit breaker ?
Why the steam turbines are run at high speed where as the hydro turbines are run at low speed?
What is the basic difference among IPS,UPS,EPS?
Whether capacitor loads can be connected for testing a diesel engine at its full load capacity? Is there any limitation of capacotir load? Which is the best load for testing DG sets?
What is inrush current? how can calculateit? what is the affect of it?
if one of the phase is failed to 3 phase IM. what will happen?
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
If the load of transformer is getting more than its rating,,,than how to overcome this problem? Suppose thee rating of transformer is 315kva and the load is going beyond than the rating say around load: 352kva... Than how can we solve this problem without deducting the load.
11 KV Power cable end earth connection insulation got burned wht is the reson pl give the resons
what irequirment need to be followed when working on live equipment
We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.
2 t/f operating in parallel will share the load according 2 their- a)leakage reactance,b)pu impedence,c)efficiency,d) rating.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)