Why we not use 2-20Ma or 1-20Ma
Answers were Sorted based on User's Feedback
Answer / sai kiran.c
very goood my dear frnd ....actualy wat u said is
rite...itzz a usualy universal standard.
BUT ALSO ONE REASON STARTING FROM 4ma IS THAT THE DEVICE
WILL WRK IN OPTIMUM RESPONSE FRM THAT RANGE.
& MOSTLY AND ALSO IT NEVR STARTS FRM ZERO BCOZ IT DOESNT
MEAN THE DEVICE IS IN REST POSITION OR NOT.
WE CANT JUDGE THE DEVICE IS IN ON OR OFF.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / j jones
Sai Kiran.c is correct is saying that we don't start from 0mA because we need a "Live Zero" this is so that if the control loop goes open circuit we have an indication of this.
why do we use 4-20mA, not 1 or 2mA - 20mA, well simply just as in a pneumatic system we use 5-15psi, (0.2-1bar) it gives us the most linear output, and above that, if we were to use 1mA, any induced voltages from eddie currents in cables running alongside could cause a mA to be produced by the resistance of the cable, so our readings would be affected, and if we amplify the signal, the amplification has to be greater as we have to amplify 1mA more than a 4mA signal
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / carl_ellis
Answer 1 is correct. The ISA SP50 standard established
4-20mA worldwide as the analog control signal decades ago.
But what the answer 1 and the others miss is that using 1 or
2 mA at the low end would not provide sufficient power to
power 2 wire loop powered instruments.
2 wire loop powered instruments use about 3.6mA at 24Vdc to
power the electronics which makes the measurement and
controls the output circuitry. That's about 85mW, not a lot
of power.
1mA or 2mA of current would provide only a fraction of 85mW
available at 4mA for powering the instrument itself, and
reduce the functionality of 2 wire loop powered instruments.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / larry thompson
As with all analog loop standards the range must be divisible by 4 so the technician can determine which quartile the signal is (25%, 50%, 75%, 100%) in. 4 mA was deemed the minimum current necessary to power most analog signal transmitters (it had previously been 10 to 50 mA)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suvankar haldar
because 4to20mA is a universal& Used mostly in all factories
| Is This Answer Correct ? | 4 Yes | 16 No |
When cryogenic control valve will be applied?
how checking is done in fiber optic cable? explain the working of RTU?
HOw To Use 24V DC in Instrument?
I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )
What is governor of turbine?
what is Dry Leg calibration and where is it used
control modes
what is isolation Transformer???...
Someone Please tell me what are the Pre-Commissioning activities in a Thermal Power Plant for an instrumentaion Engg.
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
What are the uses of orifice plates?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)