I work on a electronic positioner transmitter 4211 at the
field.I connect my multimeter in series to get the current
output then I calibrate it to 4ma in 0% of position of the
valve and 20ma in 100% position of the valve.My problem is
in the field I get the correct output current based on my
multimeter but in the dcs they only receive 40% in a output
20ma of this positioner.Then I try to simulate in this
analog card and they receive the equivalent percent on the
value that I simulated.Is ther any possibility to reset the
zero and span of this positioner 4211 fisher.And what other
possibility I can do to fixed this.This is my email add (
landicho_randy@yahoo.com )
Answers were Sorted based on User's Feedback
AI card is two wire and the electronic positioner
transmitter is also two wire. I already simulate ma directly
into the card and the DCS receive the equal percentage of
the ma that I simulated.
| Is This Answer Correct ? | 2 Yes | 0 No |
dear friend as per my opinion be sure that your trasmitter
is 4 wire or 2 wire? OR ensure about your ai card 4wire or
2 wire
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
you should check that your AI channel might consist of 3
terminals, 1+,1-, COM. this is the facility provided to
connect both voltage(0-10V) or current(4-20ma) analog signal
introducing to AI module/card.
since you are using current i/p(4-20ma) 1- & COM channels
must be looped with 250ohm resistance first. this might
solve your problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
pls suggest suitable MOC of diaphragm for pressure measurement of UREA grade solution service fluid.
what is the current pay package for an instrumentation engineer having 2 years of experience in cryogenic technology???????
What is instrumentation instrumentation engineering?
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
What is the calibration procedure of Drum level transmitter if range is 0 to -400 mmh2o in lab?
What is negative range in transmeter?
If boiler drum level transmitter is not working properly what you will do for resolving the problem in plant running condition?
Why grounding is necessary? Give example with diagram.
0 Answers Bright Point, DS Group,
Hello Friends do you know this answer of this Question? Which color you would use when there is Somthing not correct or need to change In P&ID? i mean color that use for highlight that need to update in P&ID. Yellow Highlighter ? Red color ? Blue Color ? Appreciate for your answer. Thanks Blue Color
Why went
why OPC server is used in DCS?
how to calibrate electro pneumatic positioner 8013 mil controls ltd ?gsr
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)