Answer / ramesh
NGR-Neutral Grounding Resistor.It is used to limit the
fault current in the neutral line.calculation based on fault
current in stator in generator and star side in trfr
| Is This Answer Correct ? | 25 Yes | 4 No |
Answer / ravi kumar purohit
DESIGN AND SELECTION CRITERIA OF
NGR
Neutral Grounding Resistor:
The power transformer secondary 6.6kV neutral shall be
medium resistance earthed in order to limit the 6.6kV
system earth faults to low values such as to limit
excessive damage to 6.6kV equipments.
Also that the earth faults are not too low value to cause
earth fault relay non-operation.
System voltage = 6.6kV
System voltage per phase = 6.6/√3
Vph = 3810.6Volts
Earth fault current (I) =50A for 5 sec
NGR calculation is done on the basis of following formula,
Vph= I X R
R= Vph / I
R= 3810.6/50
Resistance= 76.21 Ohms
NGR Selected is 6.6kV , 50A, 76.2Ohms, 5sec.
Normally 50 A
| Is This Answer Correct ? | 21 Yes | 3 No |
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / madivalanagaraja@gmail.co
It is similar to the ground resistor calculation for transformer
The typical example was answered earlier for transformer dt.19-06-2009
Neutral of transformer can be grounded solidly earthed OR with Neutral Grounded with Resistance.
Typical shunt calculations fro 5 MAV 11/6.6 kv transformer neutral are as :_
Transformer rating = 5 MVA
Voltage ratio = 11/6.6 KV
Vector Group = Dyn11 (6.6 KV ground through Resistor)
During Earth fault voltage between Neutral
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / a s bhandari
Ohmic value of neutral grounding resister for a transformer is calculated as follows:
R = Vph/ I where I - value of fault current to be limited to flow through the neutral path, normally it is 50A for 5 sec.
Based on above, for 6.6 kv star side of a transformer
resister value shall be 76.21ohm.
| Is This Answer Correct ? | 0 Yes | 3 No |
with out colour codeing on conductor how can be find what is r,what is b,what is y phases.....
which type motor r use in the celling fan.....
What is BUCKBOOST TRANSFORMER and Operation of Buckboost transformer?
Capacity of circuit breakers all types
why most of the modern day type electrical appliance have 2 pins rather than 3 pins?
Basic motor transformer generator
what is the unit of current
What is the formula for calculating no-load current?
what are the different type of transformers available in markets???
6 Answers Atomic Energy Commission,
How to apply 'c' license and also explain what is difference between 'c' and 'b'license.i am also working in one of the private company.i have finished my diploma in 2014 .i have already finished in ITI electrician course.....
hi,every one, i have to write the search paper on "performance policy optimization" of NGN (next generation networks). i need the material on this topic. can any body help me. please tell me any useful site where the good material is available and name of any reference book. it should be a great help for me.
What is the permissable nutral current of three phase system as per IS standards?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)