Answer / ramesh
NGR-Neutral Grounding Resistor.It is used to limit the
fault current in the neutral line.calculation based on fault
current in stator in generator and star side in trfr
| Is This Answer Correct ? | 25 Yes | 4 No |
Answer / ravi kumar purohit
DESIGN AND SELECTION CRITERIA OF
NGR
Neutral Grounding Resistor:
The power transformer secondary 6.6kV neutral shall be
medium resistance earthed in order to limit the 6.6kV
system earth faults to low values such as to limit
excessive damage to 6.6kV equipments.
Also that the earth faults are not too low value to cause
earth fault relay non-operation.
System voltage = 6.6kV
System voltage per phase = 6.6/√3
Vph = 3810.6Volts
Earth fault current (I) =50A for 5 sec
NGR calculation is done on the basis of following formula,
Vph= I X R
R= Vph / I
R= 3810.6/50
Resistance= 76.21 Ohms
NGR Selected is 6.6kV , 50A, 76.2Ohms, 5sec.
Normally 50 A
| Is This Answer Correct ? | 21 Yes | 3 No |
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / madivalanagaraja@gmail.co
It is similar to the ground resistor calculation for transformer
The typical example was answered earlier for transformer dt.19-06-2009
Neutral of transformer can be grounded solidly earthed OR with Neutral Grounded with Resistance.
Typical shunt calculations fro 5 MAV 11/6.6 kv transformer neutral are as :_
Transformer rating = 5 MVA
Voltage ratio = 11/6.6 KV
Vector Group = Dyn11 (6.6 KV ground through Resistor)
During Earth fault voltage between Neutral
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / a s bhandari
Ohmic value of neutral grounding resister for a transformer is calculated as follows:
R = Vph/ I where I - value of fault current to be limited to flow through the neutral path, normally it is 50A for 5 sec.
Based on above, for 6.6 kv star side of a transformer
resister value shall be 76.21ohm.
| Is This Answer Correct ? | 0 Yes | 3 No |
what type of motor used to move a 1 ton gate? and relate ratings with load.
what percentage of marks in B-TECH is needed for section engineering exam
How the capacitance og capacitor volatage transformer is decided?
when is the Ohms law is applicable?
what is lowest system voltage?
what is the difference between arc and spark
Is it mandatory statutory requirement of transformer oil filtration annualy despite oil is withstanding required dieelectrical strenth and all others parameters
I need HT sphere gap calibration table. Can any body help me.
what is shunt trip coil? what was the function in rmu?
what is the VVVFD and?
what are the uses and applications of rectifiers?
A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)