The formular of how to calculate a cross sectional cable to feed an electric motor.
Examle: 15KW, 26.1A, 415V. Calculate the cable size in mm2
Answers were Sorted based on User's Feedback
Answer / shridhar awasthi
Since it's an LT cable so in this case we can't apply the min cross sectional formula A=I square root t/K.
to find out the cross sectional area for this case fist find out the Load current which is given 26.01A. so refer the Manufacture cataloge and select the appropriate cable size for full Load current.
after selecting appropriate size of cable we will have to apply the derating factor according to the laying condition.
Now multiply that derating factor to cable ampacity,so we will get actual current carrying capacity of that cable.
Now for find our the no. of runs divide full load current to actual current capacity of cable after applying derating factor,so will get no. of runs.
now calculate voltage drop. if this in the permissible limit the our selection is right and if the V.d. is beyond the the increase the size of cross sectional area or no. of turns.
In this case 4 sqmm copper wire is sufficient for Star-delta starter.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jinesh bhaskaran
we have to consider the type of motor starting, cable length and RPM of the motor.
According to these criteria we can select the cable from the cable manufacturer table.
| Is This Answer Correct ? | 0 Yes | 0 No |
can any one tell me the formula to select the thickness of wire selection according to ampere rating
why can tv operate at low voltage??
why field rhoestat is kept in minimum position while armature rheostat at maximun position?
how ELCB drip when earth and phase touch together?
What safety followup during kWh meter isolation
why swityard is necessrry requirement in any bis power distributin systems?
how can we chacke adiod in a circuit
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
I BOUGHT A HAVELLS ACCL WITH GENERATOR STOP FASCILITY(i.e- BASICALLY IT IS A AUTO CHANGE OVER SWITCH) FOR MY HONDA EXK 2000S HOME GENERATOR (WHICH START IN PETROL & RUN IN KEROSENE). ACCL HAS 8 POINT. 2 FOR MAINS(PH & NUE), 2 FOR LOAD, 2 FOR GEN AND 2 FOR IGNITION POINT(X1 & X2). THE IGNITION POINT IS SPECIALLY FOR AUTO ENGINE STOP WHEN MAINS POWER RESTORE. I CONNECT THIS X1 & X2 POINT TO THE GENERATOR STATER MOTOR & EARTHING POINT. BUT WHEN MAINS FAILS THE GENERATOR COULD NOT START, BUT WHEN DISCONNECT THOSE X1 OR X2 POINT, THEN THE GENERATOR START. BUT WHEN MAINS ON THEN THE GENERATOR SHOULD START, AND WHEN I OFF THE MAINS THE GENERATOR AUTOMATICALLY STOP. PLESE HELP ME HOW I STOP THE GENERATOR AUTOMATICALLY WHEN THE MAINS RESTORE.
Can HT cable(11kv cable) be used for 415V, 700A requirement.
can we correct the p.f.of ac generator?
Iam deepthi.i completed my b.tech from electrical engineering.i want to prepare for civil services.i dont have much knowledge about these exams,but i have great zeal of cracking exams.plz provide me suggestions to which options i can select for optionals
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)