In 2 wire transmitter 1 wire is used for power and other is
used for signal( 4-20)ma
In 4 wire transmitter 2 wires are used for power and 2 wires
are used for signal (4-20)ma .
but my question is "what is the criteria or parameters we
have to consider while selecting these transmitters for eg(
distance, safety zones etc.
Answer / omer baosman
A 2 wire xmitter is powered by the mother instrument. The
output signal(4-20ma) is returned on the same wires that
powers it. the main purpose of this design is to reduce
wiring cost, standrdisation of circuits, and above all, to
kep all the transmitters at same ground potential.
A 4 wire inst. has design flexibility to utilize any power
like, 230vac, 24 vdc or 110 vac. It can feed the signal to
any mother instrument. Wherever the basic sensor of an
instrment needs power other than 24 vdc (like chemical
analyser) u have no choice but to use a 4 wire xmitter.
| Is This Answer Correct ? | 4 Yes | 0 No |
how can calibrate pressure transmeeter in the feild ?
a laways iface problem with brine level transmitter sealing diaphram a laways giving error and maximum reading i made re range and adjust with side glass but during commission it giving gap reading between it and side glass i need help from expert to explain how to calibrate it. note:dp transmitter yokogawa company
what is piezo electric transducer?its principle?
i want to make project on process control using plc.please give me idea about this.
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
How can we check Zero of DP type Level Transmitter onside?
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
The DCS stand for________________________. it is composed of the following major components: a:______________ b:______________ c:______________ d:______________
Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72
What are Sinking and Sourcing IO Cards
What is instrumentation amplifier?
What are different type of instrument cable
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)