IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN
WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED,
SO WE CAN SAY THE PROBLEM IS IN
Answer / carl_ellis
The problem is in the controller's PID tuning, which is
tuned to be too sluggish.
All of the loop's control components work properly:
- the transmitter reports the process variable
- the controller responds to an error (albeit too sluggishly)
- the control valve responds to the controller's output, as
evidenced by switching to manual mode
The PV response as reported by the transmitter depends on
the controller's appropriate response to error. If the
controller's response to error is sluggish, then the loop's
PV response will be sluggish.
Manual mode offers a means of overriding the PID's
calculated output value and driving the output to where it
needs to be.
This question qualifies as one of the best interview
questions I've read on this site. I'll be sure to use
this question when I interview candidates.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
When can a bypass not used on a positioner?
hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection
why fuse block is not used for AI signal?
What is the Difference between CNC and PLC
relation between level and differential pressure.
what is bms?
i want use pressure transmitter for flow ,how?
what is the exact job for automation enggineer?
what is the tempareture conpensation?what is the use of this?
what is easiest way to read STL language in PLC?
Good Evening all.My question is - For a feed water line to an equipment if i need to measure the flow we will use orifice /magnetic/vortex depend on cost/spec.If i need to measure a ''Alarm''signal and ''Interlock'' from one point i think we can use orifice type in one location with 2 different tapping points - one for alarm and one for an interlock to flow valve..If in case i need to have both these signals(Alarm & interlock) from magnetic flow meter,is it possible??will 2 seperate sensors will be located inbuilt r we can program it ??..i thk we can have one transmitter with these 2 signals...need to know any technical issues are there?pls clarify
Explain bernoulli’s theorem. State its application.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)