Answer / naveed

we can not calibrate radar level transmitter only add jest parameter empty calibration,full calibration,blocking distance ,safety distance and other parameter.

Is This Answer Correct ?    49 Yes 5 No

how can we calibrate RADAR LEVEL transmitter 0% to 100%..

Answer / sam

You need to be more specific in your questions but I assume
you are referring to the frequency modulation radar (cone
type) and not the wave guide pulse radar (TDR).

This is a very generic procedure, use your radar's vendor
manual to do the calibration.

Take a measuring tape and measure the actual distance from
the cone to the zero position and the 100% position in your
vessel. If it is a closed pressurized vessel use the design
engineer's internal vessel drawings. If all else fail use
the dimensions of the vessel itself to determine what and
where z/100% is on the vessel. Use the vendor manual to see
how to use these measurements. It might be as simple as
entering these values directly as your z/100% calibration
values or you might have to do a small calculation like
maximum possible distance (tank depth) minus z measured
distance equals zero distance, and maximum possible (tank
depth) distance minus 100% measured distance equals 100%
distance.

Also keep in mind radars are distance measuring instruments
and not level measuring instruments and the fact that the
distance measurement is the exact opposite of level in
relation to the total distance measurement. This means if
your tank total distance is 3 meter (assuming tank bottom is
also zero position) and your radar measures a DISTANCE of 2
meters to the top of your product in the tank, the actual
LEVEL in the tank is only 1 meter.
It is easy to look at the disply on the radar and think this
is your actual level measurment. You therefore need to
modify the local display to indicate level in mm or %, as
well as setup your output to level and not distance after
the calibration. The radar will then give out 4mA when the
tank is empty as per example above and 100% as the tank fill
up with product to the point where you have specified 100%
should be. If your output is setup for distance it will
output the exact opposite. Watch out!!

If you need a vendor manual download it from the internet.
Good luck

Is This Answer Correct ?    45 Yes 3 No

how can we calibrate RADAR LEVEL transmitter 0% to 100%..

Answer / kathirselvam

we can calibrate the level of radar by blocking the way of
radar path

Is This Answer Correct ?    9 Yes 14 No

Post New Answer

More Instrumentation Interview Questions

cascade controller is feed back or feed forward or both

4 Answers  


why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .

1 Answers   Flour Tech Engineers (P) Ltd,


Capacitance, resistance ( colour coding ), parallel & series circuits.

0 Answers   CCIE,


define SIMULATION a and what is the need of it

3 Answers   Siemens,


We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.

1 Answers   Shyam Steel,






What is the Flow rate ?

2 Answers  


what is weighfeeder

2 Answers  


WHAT IS DIFFERENCE BETWEEN TWO WIRE RTD AND THREE WIRE RTD?

5 Answers   Yokogawa,


What is difference between reset and initialization in system.

1 Answers   Marafiq,


How to Calibrate Vortex Flow transmitter in field

0 Answers  


What is flow ,level, pressure transmitter ?and units?

2 Answers  


How a oxygen sensor & analyzer work at boiler or furnace, whats the principle & science is beyond this,How O2 sensor sence & convert signal & move toward analyzer & analyzer show reading in percent?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)