You need to be more specific in your questions but I assume
you are referring to the frequency modulation radar (cone
type) and not the wave guide pulse radar (TDR).
This is a very generic procedure, use your radar's vendor
manual to do the calibration.
Take a measuring tape and measure the actual distance from
the cone to the zero position and the 100% position in your
vessel. If it is a closed pressurized vessel use the design
engineer's internal vessel drawings. If all else fail use
the dimensions of the vessel itself to determine what and
where z/100% is on the vessel. Use the vendor manual to see
how to use these measurements. It might be as simple as
entering these values directly as your z/100% calibration
values or you might have to do a small calculation like
maximum possible distance (tank depth) minus z measured
distance equals zero distance, and maximum possible (tank
depth) distance minus 100% measured distance equals 100%
distance.
Also keep in mind radars are distance measuring instruments
and not level measuring instruments and the fact that the
distance measurement is the exact opposite of level in
relation to the total distance measurement. This means if
your tank total distance is 3 meter (assuming tank bottom is
also zero position) and your radar measures a DISTANCE of 2
meters to the top of your product in the tank, the actual
LEVEL in the tank is only 1 meter.
It is easy to look at the disply on the radar and think this
is your actual level measurment. You therefore need to
modify the local display to indicate level in mm or %, as
well as setup your output to level and not distance after
the calibration. The radar will then give out 4mA when the
tank is empty as per example above and 100% as the tank fill
up with product to the point where you have specified 100%
should be. If your output is setup for distance it will
output the exact opposite. Watch out!!
If you need a vendor manual download it from the internet.
Good luck
| Is This Answer Correct ? | 45 Yes | 3 No |
Answer / kathirselvam
we can calibrate the level of radar by blocking the way of
radar path
| Is This Answer Correct ? | 9 Yes | 14 No |
Why capacitive banks ar5e important?
please tell no. & add. of consultancy who recruit me in power plant as instrumen engg. present i m working in power plant as ass.t instrument engg. thanku mahesh 09226562826
What is the difference between HMI and MMI?
Why some transmitter shows flow in MMWC and some in TPH?
how does we do bench calibration of a differential transmitter.
how many types of viberation transmitter and how to calibrate and where use of vibration transmitter
How to calibrate Magnetic flow Transmitter in Field
What is an antisurge control system, how it works?
1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling
hi i am eswar i want to know the instrumentation interview questations for eil(engineers india ltd) i have applied for engineer post in eil please help in this.my mail id eswar310@gmail.com
What is Difference between PLC and CNC ?
the output of the common trasmitter protocol in qatar gas are the following
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)