why transformer ratings in kva?
Answers were Sorted based on User's Feedback
Answer / princealekota
Since transformer is a static there will not be any
rotational losses it have only iron loss depend upon
voltage and copper loss depend upon current
for AC supply systems like generator, transformer rating is
done in KVA because of inductance present in AC . we don't
know load is resitive or inductive
so we will take load KW=KVA,
power = voltage*current*cos(pi)
if load isinductive cos(pi) have some value less than 1
if load is resistive cos(pi)is 1
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / karthik
Basically any rotating machine depends up on power factor
and other rotational losses. Transformer is not a rotating
machine and transformer losses depends on only Iron losses &
Copper losses. Iron losses depends on voltage and Copper
losses depends on current. these losses not depends on power
factor. So Transformer rating measured in KVA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / purushotham
In transfromer the core loss depends on volatage and cu
loss depnds on current so the both are voltage and current
(VA) so the tranformer rating is in Kva.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradyumna chandra panda
Why the motors are rated in KW and transformers are rated in
KVA?
Ans . Motor is a consuming device it consume the power
(wt) so it is rated in KW. But the
Transformer is a static device which transfers
the power (Apparent power) from the
Generating point to the user. Apparent power is
the product of voltage and current
I.e. Increase voltage with decrease current and
decrease voltage with increase
current. Power factor of the load does not
affect apparent power it affect the Active
Power.
Active power is the real power which the transformer
gives. Transformer should not be rated on the base of
Active power (KW) which is variable because the power factor
of the load is not knows before which to be connected across
the transformer.
Reactive power Apparent power (k)
KVA
VI sin Q k
Kw
Q q
Active power VI cos Q
Active power is equal to apparent power at resistivity load
where power factor is unit at cos Q is equal to zero degree.
Active power is decrease power where cos Q (not fi) is
increase
Therefore in simple we can say due to unknown power factor
transformer and generator are rated in KVA.
Hint – we know cos FI is the value of cos Q i.e. apparent
power/ active power
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / s saranraj(sri durgadevi polyt
Both the losses of the transformer is independent of the
power factor (cos phi), which means a transformer would not
make any change in the power factor, since both the losses
viz copper loss(depends on current) and iron loss(depends
on voltage) are independent of power factor, that is why a
Transformers rating is not on kW, but on KVA
(or)
because,ironloss is depends in voltage and cu_loss is
depends in current.so the transformer ratings in kva
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vignesh
Thumb Rule - all AC power sources - Generators,
Transformers, UPS etc. are rated in KVA and all loads are
rated in Watt or Kilowatt..
AND hence there is no need of power factor.
KVA=V X A (FRO SINGLE PHASE TRANSFORMER)
KVA = 1.732 X V XA (FOR THREE PHASE TRANSFORMER)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / m. jamshed
As transformers are the power source and every power source
is deigned for specifid value of current and voltage.
The amount of current in A/C circuits is greatly affected
by p.f.as if we take two examples for the same kw with
different p.f we will get different amount of current that
is high current for low p.f and vice versa.
For the transformers we do not know about the load p.f,so
it will be rated in kva to determined the exact value of
current it can provide.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manikanta..{munna} geethanjali
load is something which dissipates energy..!! in case of
transformer , ideally a transformer is power source
device...and but this acts as load practically bcoz of
losses in it...!!!
coming 2 d rating any load is alwayz rated in kw..!! here
in a transformer the losses are due 2 copper and iron which
depend on current and voltage respectively...there fore v
rate the transformer in v*i !!!! and they is no use of
including powerfactor.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / aryan
Since transformer is a static there will not be any
rotational losses it have only iron loss depend upon
voltage and copper loss depend upon current
for AC supply systems like generator, transformer rating is
done in KVA because of inductance present in AC . we don't
know load is resitive or inductive
it is independent there fore it is measured in kva
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hitesh g. dobariya
kVA is the unit for apparent power. Apparent power consists of active and reactive power. Active power is the share of the apparent power which transmits energy from the source (generator) to the user. Reactive power is the share of the apparent power which represents a useless oscillation of energy from the source to the user and back again.
It occurs when on account of some inertia in the system there is a phase shift between voltage and current. This means that the current does not change polarity synchronous with the voltage. But the heat generated in a winding as well as the eddy current losses generated in a transformer core depend on the current only, regardless of whether it aligns with the voltage or not.
Therefore the heat is always proportional to the square of the current amplitude, irrespective of the phase angle (the shift between voltage and current). So a transformer has to be rated (and selected) by apparent power.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the difference between AC choke (inductor) and DC choke (inductor), working and design point of view?
What will be happend if we not ground CT secondary?
3 Answers Enercon, Engro, THDC,
Pls tell me whether we can use EN3A material for shafts of Permanent magnet alternator.What will be the effect of magnetic and nonmagnetic material for shafts on magnetic properties of PM rotor .
how much amps will get from a 360/11kv line
what is the suitable voltage of transmission line to transmit 10000w power through 250 km. (a)11kv (b)33kv (c)66kv (d)132kv ]and please tell me whats the logic behind it
I have a transformer 3phase 11kv/410v and its name plate missing. now how can I judge its rated kva?
How to operate a ac chilar plant?
why ligthing is not available in switch yards?
Why does inductor is connected to dc supply? or what is the role of an inductor when connected to DC source?
In 11KV Double pole structure for each phase we are using Disc one Insulator. Why we are not using 2 r above insulators instead of one insulator?
why neutral of 6.6 kv star connected sq. cage induction motor does not get earthed, though for earth fault protection it is must.
How to determine alternating current frequency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)