after syncnhronistion how generator speed controlled by grid
Answers were Sorted based on User's Feedback
Answer / arjunyadav
the generator speed cannot varied ofter synchronisation
because if the speed varies then the frequency varies if we
change the speed then the over or under frequency relay
will operate and trips the circuite.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
The grid is more powerful than the generator or the
station.The speed of any generator is decided by the grid
while synchronizing or running.3 % variation in frequency is
allowed as per IE rules.
Is This Answer Correct ? | 2 Yes | 1 No |
The generator is magnetically coupled to the grid
frequency. If the fuel to the generator is increased the
generator will try to increase speed but as it is
magnetically locked to the frequency it will take more load
instead. The reverse will happen if the fuel is decreased.
Under some circumstances the magnetic coupling can be
broken. If this happens the energy from the grid will try
to drive the generator back into synch. This can cause
extensive damage to the generator and/or switchgear.
Therefore protection should be used to stop this from
happening.
Is This Answer Correct ? | 0 Yes | 0 No |
How ElCB tripping if Neutral touch with ground
How to identify the whether its an isolator or Breaker in MDB
What do you mean by isolators and circuit breakers?
6 Answers Bhushan Power Steel,
to improve the existing power factor whether capacitors have to be added in series or parallel.and why
how much current capacity 250 amp. mccb please tell me about whats are the reasons to trip 2 or 3 times in a night. and what are the steps to short out this problem
what are the steps involved in generator load test?
difference between relay and solenoid?
Why we use 2core cable for Dc motor.Can I use 3core?
5 Answers JK Paper, Maharaja Whiteline,
what is busbar. how many types of starter.what appartus will be used to improve voltage.what is the function of starter.what is b.h.p.what material is used for earthing.
which meter used to measure a flus
make control wire diagram of start and stop a function with a single push button
How does "OUT OF STEP" relay ,for Synchronous motor protection, work?