after syncnhronistion how generator speed controlled by grid
Answers were Sorted based on User's Feedback
Answer / arjunyadav
the generator speed cannot varied ofter synchronisation
because if the speed varies then the frequency varies if we
change the speed then the over or under frequency relay
will operate and trips the circuite.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
The grid is more powerful than the generator or the
station.The speed of any generator is decided by the grid
while synchronizing or running.3 % variation in frequency is
allowed as per IE rules.
| Is This Answer Correct ? | 2 Yes | 1 No |
The generator is magnetically coupled to the grid
frequency. If the fuel to the generator is increased the
generator will try to increase speed but as it is
magnetically locked to the frequency it will take more load
instead. The reverse will happen if the fuel is decreased.
Under some circumstances the magnetic coupling can be
broken. If this happens the energy from the grid will try
to drive the generator back into synch. This can cause
extensive damage to the generator and/or switchgear.
Therefore protection should be used to stop this from
happening.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is difference between the buscoupler and bus raiser?
when the direction of a 3phase induction motor is reversed , is there any losses increases?
Why DC current is not used in transformer?
why a motor rating in KW?
i wanna know that star point in transformer becomes as a neutral on secondary side now tell me that how is that possible?because if joit the all three winding ends with each other it can b short circuited.dut it doesn't.WHY?pls Answer me in brief.thanks alot
what is the principal of starting of a three phase induction motor.
why do we use bundle conductors instead of using single conductor of larger size for high voltage transmission?
when we gave dc supply to 220v dc motor its rpm is 1200. then we gave 180v. how many rpm of its motor. gave answer with calculation at my ID.... ravizak@ymail.com
what is meant by real power,active power,reactive power & apprent power ?please explain it?
why transmission line 11Kv OR 33KV,66Kv not in 10kv 20kv?
43 Answers A2Z Group, Baiji Power Plant Gas, Electrical, HCL, Kirloskar, Mepco, NEPC, OAMC, UNI, University of Lahore,
if the power factor is .88 i want to increase the power factor to .99 what number of capacitor is to add?
Why RCD trips on connecting to one Socket but not trips one other circuit on same RCD.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)