hi can you give any body fault level calculation, generator
fault level calculation,transformer fault level calculation
for system fault level with equation? i have 3.3kv
generation voltage three gas gen sets, one is 1.9MW,2nd is
2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one
gas gen sets is 3.8MW, we are step up to 22kv by transformer
Answers were Sorted based on User's Feedback
Answer / baban mungase
Fault level of transformer = (MVA)/(%of impedance X 1000)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dhiren
Hello Rajeshbhai,
You have not mensioned the capacity & impedance of the
transformer
for example if we have
A 5MVA, 11/22KV transformer with a 5% impedance.
Maximum fault MVA will be
5MVA/0.05 = 100MVA
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / deltawye
can you give me the exact details & specification like
impedances,power rating service factor etc. of transformer
and generator before we can answer it ...
Is This Answer Correct ? | 1 Yes | 1 No |
What is difference between dc three point starter and dc four point starter?
How energy is generated in hydroelectric power plant?
l&t switch FN 63 handle position can we change
what is the difference between ground, earth and neutral?????????....
what are the range of memory address in plc for L&T lx7 4A
what is power and what is watts detailed description and formulas
How many loops can be provided in a circuit as per IS rules.?
We have 90mX100m hangar with 16 no.of supporting pillar. It is required to provide power supply on all pillars. what is suggested earthing scheme for hangars.
what is load cell? whrere its used ? how to measured?
how electical engineer is related to apsrtc (general) post? if they ask a question in interview as why did u choose this job what shd be answer
how to maintain standard votage in power system?
What is balance beam relay ?