hi can you give any body fault level calculation, generator
fault level calculation,transformer fault level calculation
for system fault level with equation? i have 3.3kv
generation voltage three gas gen sets, one is 1.9MW,2nd is
2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one
gas gen sets is 3.8MW, we are step up to 22kv by transformer
Answers were Sorted based on User's Feedback
Answer / baban mungase
Fault level of transformer = (MVA)/(%of impedance X 1000)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dhiren
Hello Rajeshbhai,
You have not mensioned the capacity & impedance of the
transformer
for example if we have
A 5MVA, 11/22KV transformer with a 5% impedance.
Maximum fault MVA will be
5MVA/0.05 = 100MVA
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / deltawye
can you give me the exact details & specification like
impedances,power rating service factor etc. of transformer
and generator before we can answer it ...
| Is This Answer Correct ? | 1 Yes | 1 No |
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
what is the effect of power factor in electrical circuit ? if we mainten power factor near about unity (0.999) our energy consumption Units increase or decrease?
11 Answers Piramal Healthcare,
are there rmu for 3 transformer?
assume we are put both df/dt and vector surge relay in same bus the df/dt relay setting is +5 hz an -5HZ. we want operat the vector surge relay before the df/dt how i calculate the setting of the vector surge relay.
Why use in ht motore
What is the use of iron core in a transformer?
how to calulate transformer secodary fault A?
What is duty cycle for HT motors? How many start permitted if mentioned as 01 for hot and 02 for cold per duty cycle?
Can anyone explain me about the RLC based Impulse high voltage generator and how to and operation of Series resonant High voltage reactor...?
when a 500kva-400hz single phase transformer operated on a 100hz supply then what will be kva required
We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?
Why i receive the GCU fault in my DG Sychronization panel . what all the factors considered for this fault .
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)