why transformer ratings in kva?..

Answer / jjj

There are 2 losses in transformer. One is copper loss which depends on current and the other is iron loss which depends on voltage. These two factors are not affected by the power factor. This is why transformers are rated in KVA and not KW. Single phase KVA = Amps x Volts/1000. Single phase KW = Amps x Volts x pf/1000. 3 phase KVA = Amps x Volts x 1.73/1000. 3 phase KW = Amps x Volts x 1.73 x pf/1000.

Is This Answer Correct ?    0 Yes 0 No

why transformer ratings in kva?..

Answer / tarun aggarwal ymca

We know that Transformer rating may be expressed in kVA as well as Generator and Alternator rated in kVA
There are two type of losses in a transformer;
1. Copper Losses
2. Iron Losses or Core Losses or Insulation Losses
Copper losses ( I²R)depends on Current which passing through transformer winding while Iron Losses or Core Losses or Insulation Losses depends on Voltage.
So the Cu Losses depend on the rating current of the load so the load type will determine the powerfactor P.F , Thats why the rating of Transformer in kVA,Not in kW.
Designer doesn’t know the actual consumer power factor while manufacturing transformers and generators i.e. the P.F (Power factor) of Transformer and Generator/Alternator depends on the nature of connected load such as resistive load, capacitive load, and inductive load as Motors, etc.
But Motor has fixed Power factor, i.e. motor has defined power factor and the rating has been mentioned in KW on Motor nameplate data table. That’s why we are rated Motor in kW or HP (kilowatts/ Horsepower) instead of kVA.
In addition, Motor is a device which converts Electrical power into Mechanical power. In this case, the load is not electrical, but mechanical (Motor’s Output) and we take into the account only active power which has to be converted into mechanical load. Moreover, the motor power factor does not depend on the load and it works on any P.F because of its design.

Is This Answer Correct ?    0 Yes 0 No

why transformer ratings in kva?..

Answer / altaf chhimpa

Any device is rated depending on losses of the machine. In a transformer the losses are iron losses which depends on voltage and copper losses which depends on current so there are no losses which depend on power factor hence transformer is rated in KVA.

Is This Answer Correct ?    0 Yes 0 No

why transformer ratings in kva?..

Answer / sagar sahu

1.The transformer losses of depends upon iron and copper losses depends
voltage and current .
2. The load which connected on the transformer is in terms of k/w, iron and copper losses depends voltage and current so the transformer rating in KVA.

Is This Answer Correct ?    0 Yes 0 No

why transformer ratings in kva?..

Answer / sagar sahu

The transformer is losses is two types
1. copper loss
2. iron loss
The voltage while the copper loss upon the current

The load which connected on the transformer is an terms k/w

Iron loss and copper loss depends upon the voltage and current so the transformer rating is an KVA.

Is This Answer Correct ?    0 Yes 0 No

why transformer ratings in kva?..

Answer / higiro peter gakwavu

Transformer losses, are copper, iron losses but some times
comes in leakeges. Which some times are negligable.
And mostly, copper losses take alarge portion due to
transformer windings.
kW is for loads, whose losses are normally known to be
caused by heat or I2R, so due to location and the task to be
serviced by atransformer, the power is whole, Apparent
power. As it should meet both inductive, capacitive, and
even resistive equipments in the system.

Is This Answer Correct ?    0 Yes 1 No

why transformer ratings in kva?..

Answer / dawa

since in case of transformer there is two type of losses i.e
iron and copper loses and they depends on the voltage n
current respectively and its independent of power factor so
transformer r always rated as kva and not in watt and kw

Is This Answer Correct ?    0 Yes 1 No

why transformer ratings in kva?..

Answer / sarath

yes,it is in KVA due to some constant losses

Is This Answer Correct ?    0 Yes 1 No

why transformer ratings in kva?..

Answer / gokulkrish

both cu loss and iron loss are indepentent to power factor

Is This Answer Correct ?    0 Yes 1 No

why transformer ratings in kva?..

Answer / priya

because the copper loss can be expressed only in terms of
voltage and ampere

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

What is the PIU.

1 Answers   Jindal,


How to calculate impedance volt in Transformer?

1 Answers  


WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?

1 Answers  


i am studying in final year can i allowed for 23rd UES of Indian army

1 Answers   TCS,


Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?

1 Answers   NTPC,


what are the breakdown voltage rating of mini- curcuit'transfarmer!

1 Answers  


why do we connect droop ct{in gensets}in y_phase only

2 Answers  


hello friends.. I have a doubt regarding the operation of dc machines.. I studied in a text book that a dc machine can be used as a generator and as a motor.. is this possible? If so,please send me the info about this topic.. you can also send your info to my mail.

1 Answers   Bhel, CVL,


why does connected a indutor with mnsformeretering core of current transformer ?

1 Answers  


what the different between earthing and grounding?

4 Answers  


What happens instead of using 3 phase, if we give loop of single phase to all three phases ??

1 Answers  


why C T secondary are rating 5A generaly .

7 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)