why transformer ratings in kva?
Answers were Sorted based on User's Feedback
Answer / saranraj
Transformer Both the losses of the transformer is
independent of the
power factor (cos phi), which means a transformer would not
make any change in the power factor, since both the losses
viz copper loss(depends on current) and iron loss(depends
on voltage) are independent of power factor, that is why a
Transformers rating is not on kW, but on KVA
because,ironloss is depends in voltage and cu_loss is
depends in current.so the transformer ratings in kva
| Is This Answer Correct ? | 18 Yes | 5 No |
Answer / girish kumar samal, hindalco,h
actually rating of a equipment depends upon heat , which
depends upon loss. as in transformer both copper loss &iron
loss dont depend upon power factor . so transformer rating
is in kva.
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / guest
ironloss depends on voltage and cu_loss
depends current.so the transformer ratings is in kva
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / love007
iron loss depend upon vtg & cu loss depend upon current
it threrotical also
we don't know load is pure resitive or inductive
so Xmer rating in KVA
b'coz in res load KW=KVA, inductive KVA=KW/COSpi
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / mahamuni raja
copper losses of a transformer depends on CURRENT and irons
of a transformer depends on VOLTAGE not an phase angle
between voltage and current. that is why transformer rating
in KVA not an KW.
| Is This Answer Correct ? | 40 Yes | 33 No |
Answer / asfaq
Transformer has two types of losses and they are iron loss &
copper loss.Iron loss depend on voltage while copper loss
depend current,also power factor is independent of both
losses.so rating is in KVA.one more reason is that we dont
know which type of load is connected to transformer.
Power=Voltage*Current*Powerfactor
Power factor is different for different typrd of load
so rating is KVA as per my knowledge
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / vijay saharan
the cu losses rating in curent and iron losses rating in
voltage so the both losses are trnsformer and this is the
cause trasformer rating in kva.
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / suresh
kVA is the unit for apparent power. Apparent power consists
of reactive and active power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It
occurs when on account of some »inertia« in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only, regardless of whether it
aligns with the voltage or not. Therefore the heat is
always proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
| Is This Answer Correct ? | 14 Yes | 10 No |
Answer / ravi r estake
Because losses of transformer is dependent on current &
voltage probably copper & core losses.
| Is This Answer Correct ? | 15 Yes | 11 No |
Answer / amr mobarak
so For Active Power the Equation will be
P (primary) = P (secondary ) + P cu Losses + P iron Losses
Which can't describe our transformer with certain value in
both primary & secondary
| Is This Answer Correct ? | 7 Yes | 4 No |
What is AVR? Explain the function AVR?
How much Fault current can be contributed by a motor?
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
Which of the following connection is best suited for 3-ph, 4 wire system A delta-delta B star-star C delta-star D star-delta
Why converter duty transformer neutrals are not earthed...i am still not sure if this question is also correct...Please email at ranjan120482@gmail.com
if one of the phase is failed to 3 phase IM. what will happen?
in general it is observed in power stations, the tertiary winding is used in higher rating Y-Y auto transformer but not in Y-Y power transformer. is the tertiary winding is compulsory then why it is not using in power transformer
if you are in a software company,then why do you want to come in a core company like sail, ntpc(where lots of trouble like tension but you have a good life in a it company) ?
how does directional relay work incase of ac ?
What is a unit of gravity (Battery)
what type of motor are there in megger how they work.
how to calculate generator capacity?(kva)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)