Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Generally In transformer Tap Changer on HT side, but I have
seen in 66KV side in 220/66 KV, 100 MVA, Areva make
transformer. Why ?

Answers were Sorted based on User's Feedback



Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / ajay kumar

Maximum tap changer connected in HT side because due to
high voltage current level will be low and during operation
of OLTC low current will pass and there will be less risk
to operate on load

Is This Answer Correct ?    4 Yes 0 No

Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / prodip kr. paul

The purpose of OLTC is to regulate the output voltage
constant as per rating plate, but the incomer supply
voltage is variable in kind, so as per incoming supply
voltage the winding turns are selected according to voltage
per turn designed by maker and as per available incoming
voltage incoming side of transformer winding turns are
selected, means OLTC fitted in primary side, it may be LV
or HV side.

Is This Answer Correct ?    2 Yes 0 No

Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / latika

Where tap changing in the primary may hamper other
equipments there tap changing in the secondary is preferred
in power transformer.

Is This Answer Correct ?    2 Yes 1 No

Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / intekhab

it is depends on where it is used. if 66kv is in grid side
then it must have to be controlled in 66kv side.

Is This Answer Correct ?    1 Yes 0 No

Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / gaurav

Check again it will be in Ht
side only.

Is This Answer Correct ?    1 Yes 0 No

Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / gunasekaran

1.conductor size is less
2. from oltc reactive power compensation is compensate the
line loss

Is This Answer Correct ?    0 Yes 2 No

Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MV..

Answer / kesaavan

Both sides are ht (py and sy).thats why they are fix
tapchanger in sy side.

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

where induction generator is used ?

1 Answers  


wht is the purpose of the earth electrode other then earthing

1 Answers  


What is your favorite aspect of the engineering field?

1 Answers  


why impudance relay used for medium transmission power system? why not others?

0 Answers  


I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions

0 Answers  


prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system

0 Answers  


what is recovery voltage & transient voltage ?

1 Answers   Bhel,


in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel ?

2 Answers  


What is the differance between Digital Energy meter & Static energy meter? why the KWH diferance between both meters.

3 Answers   Raychem RPG,


what is the working principle of tube light?

2 Answers  


Is there any specialised book to refer about fault level calculation both in MV and LV side??

0 Answers  


why reactive power produce in generator? why inductive load absorbe reactive power?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)