why ac generator ratings in kva only why not kw ?????????????
?
Answers were Sorted based on User's Feedback
Answer / mahavir jagdev
Because you don't know what power factor the generator will be loaded with. The KVA denotes the Voltage and the Current the generator can take at resistive load.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / raul
the designs and ratings of electric machines such as
alternators, transformers etc are always decided by the
amount of losses taking place in d machines i.e. core loss
and copper loss. since the core loss depends upon the
applied voltage and copper loss depends upon d load
current, therefore the product of these dependent variables
i.e. voltage and current i.e. KVA is the acutal ratings.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / at
Not only generator but UPS / Transformer or any other
device which is giving Electrical power as output is rated
in kVA. The reason is that it is power that will be given
by the machine apperently. however when the load is
connected say for example a motor the actual power which is
converted to work is diffenrent known as active power and
involves power factor. There fore all machines with
mechnical output are rated in kw.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / s a s i
rating means max capability of sym.it will obtain from
nether voltage nor curent with resistance known facor.but
kw not provides voltage r current.it gives only wattage
only.so it will rated in kva..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amit kumar
due to two losses iron loss and copper loss.iron losss
measured in volt where as copper loss is measured in
current.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sunil
ac generator or any ac machine have two powers real and
reactive power. va or kva is the apparent power of the
machine which is near to the real power and best describes
the capacity.
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / murari.soma sekhar
THE RATING OF ANY MACHINE IS DEPEND ON LOSSES DISUPATION OF
THAT MACHINE.SO IN CASE INCASE OF ELECTRICAL MACHINE THE
LOSEES ARE COPPER LOSES @IRON LOSSES BOTH RESULT IN
DISUPATION OF HEAT .HENCE THE CU LOSS DEPEND ON CURRENT
@IRON LOSS DEPEND ON VOLTAGE.SO THAT PRODUCT GIVES RATING
OF MACHINE.
| Is This Answer Correct ? | 0 Yes | 3 No |
what is the usage of microcontroller in the panel board?
When geneartor is running in poor lagging side power factor its excitation current increases then it is running in improved lagging side.Kindly tell me when gen is running in leading side what will happen
What is HVAC, PLS SEND DETAIL OF hvac.
what happends when an isolater is operated on on-load
What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?
Can any body tell me what is use of END OF LINE RESISTOR in fire alaram circuit?
in a silicon diode we can measure .7v in a voltmeter.but why we can't use this voltage for using?
what is the voltage equation of 240/12 v transformer??
if z transform lies in ROC then. a)system is stable b)inverse of system is stable c)both system and its inverse are stable.
arrange to send solved question and answer its easy to study and understand the thing, because of Exam is to be conducted shortly
How do we check transformer losses and what are the ways to minimise it.
How to know motor winding is star or delta connected without see the information table and winding connection ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)