why ac generator ratings in kva only why not kw ?????????????
?
Answers were Sorted based on User's Feedback
Answer / mahavir jagdev
Because you don't know what power factor the generator will be loaded with. The KVA denotes the Voltage and the Current the generator can take at resistive load.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / raul
the designs and ratings of electric machines such as
alternators, transformers etc are always decided by the
amount of losses taking place in d machines i.e. core loss
and copper loss. since the core loss depends upon the
applied voltage and copper loss depends upon d load
current, therefore the product of these dependent variables
i.e. voltage and current i.e. KVA is the acutal ratings.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / at
Not only generator but UPS / Transformer or any other
device which is giving Electrical power as output is rated
in kVA. The reason is that it is power that will be given
by the machine apperently. however when the load is
connected say for example a motor the actual power which is
converted to work is diffenrent known as active power and
involves power factor. There fore all machines with
mechnical output are rated in kw.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / s a s i
rating means max capability of sym.it will obtain from
nether voltage nor curent with resistance known facor.but
kw not provides voltage r current.it gives only wattage
only.so it will rated in kva..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amit kumar
due to two losses iron loss and copper loss.iron losss
measured in volt where as copper loss is measured in
current.
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sunil
ac generator or any ac machine have two powers real and
reactive power. va or kva is the apparent power of the
machine which is near to the real power and best describes
the capacity.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / murari.soma sekhar
THE RATING OF ANY MACHINE IS DEPEND ON LOSSES DISUPATION OF
THAT MACHINE.SO IN CASE INCASE OF ELECTRICAL MACHINE THE
LOSEES ARE COPPER LOSES @IRON LOSSES BOTH RESULT IN
DISUPATION OF HEAT .HENCE THE CU LOSS DEPEND ON CURRENT
@IRON LOSS DEPEND ON VOLTAGE.SO THAT PRODUCT GIVES RATING
OF MACHINE.
Is This Answer Correct ? | 0 Yes | 3 No |
what are the maximum available current, voltage ratings and switching speeds of the power electronic devices thyristor, power mosfet, igbt, and mct?
What is electrical diversity factor in electrical installations?
how to check capacitor in general
what is errection pcbs?
advantage of using 110v than 230v
why in scott connection of transformers, main transformer is tapped at 50% and teaser transformer at 86.6%?
5 Answers Bhel, Bosch, College School Exams Tests, Wipro,
Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?
What are the typical values of characteristic impedences of overhead line and underground cabel? Why there is so much variation?
How to calculate the copper in HT motors if KW, RPM & Voltage is given
0 Answers Control Dynamics, NTPC,
Why the isolation treasforfer are connected at out put of the ups ig 200kva ??????????????????
How to calculate voltage drop in copper and aluminium cable? I have laid 240Sq.mm Aluminium cable for the length of 600 Mtrs in 1 Mtrs underground. Normal load is 150A. Transformer is 630KVA, 6.KV/433V. But, I am getting only 395 Volts when load. How to calculate voltage drop and what is the permissible voltge drop for this circuit?
Can I use measuring current transformers in protection purposes?