a distribution transformer(3 phase)supplying 440volt per
phase.now suppose one of phase voltage(230volt) becomes
zero.what will be the cause ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If other 2 phases are OK ,it may be due to open circuit in
that phase.If other 2 phases show 50% ,it may be due to one
phase missing in the primary of substation power transformer
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / ambai algates
if 1 phase open the unbalance current is flow through
neutral , so its exit the setting bkr trip .if there no
load you got 230v only in phase to open phase
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / akash`
check your high tension line d.o.if three d.o. is ok then
substation problem not coming one phase means single phasing
problem call it
Is This Answer Correct ? | 0 Yes | 2 No |
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
Determine a suitable number of slors and conductors per slot for the starter 1 winding of a 3 phase, 3300 V. SO Hz 300 rpm alternator. The diameter is 2.3 m
at which places we use 6.6KV Transformers and Motors
What is touch potential and step potential?
In transformer which temp should be less oil temp are winding temp?
why the undervoltage relay's interlock is used in earthswitch closing operation of the 400kV line scheme?
wat is the need of capacitor on aceiling fan?
in ceiling fan and table fan what is the rotating part and what is the stationary part?
what is the difference between KW and KWh?
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
A 30KW motor running at 1450 rpm draws 56A, how would you determine if this is correct or not?
why are the transmission lines operated at 220 kv nly... nt les dan dat...