Why we Specify Transformer rating 433 V Instead of 415V
?
Answers were Sorted based on User's Feedback
Answer / n. ramesh
Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.
| Is This Answer Correct ? | 46 Yes | 6 No |
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
To compensate Voltage drop at receiving end
| Is This Answer Correct ? | 42 Yes | 12 No |
Answer / ash
433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.
| Is This Answer Correct ? | 18 Yes | 6 No |
Answer / sagar surve
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / gopalen sv
When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / andy d
It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / percy
433 IS LILNE TO LINE VALUE OF 250
415 IS NOT DIVISIBLE BY 1.732
| Is This Answer Correct ? | 3 Yes | 52 No |
why a pilot exciter is used in combination with the main exciter? why not only a main exciter is used for excitation to an alternator?
what is the suitable voltage of transmission line to transmit 10000w power through 250 km. (a)11kv (b)33kv (c)66kv (d)132kv ]and please tell me whats the logic behind it
WHAT HAPPENS IF STARTER OF A FLUROSCENT LAMP IS SHORT CIRCUITED AND WE PUT THE SUPPLY ON?
what is neutral?
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
wat is the criteria we use the diff. relay ?
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
what is anode and cathode??
what are the causes for strip heater failure ?
Difference between control junction box (cjb) and power junction box(pjb)?
explain working of differential protection for a transformer?
WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)