Why we Specify Transformer rating 433 V Instead of 415V
?
Answers were Sorted based on User's Feedback
Answer / n. ramesh
Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.
| Is This Answer Correct ? | 46 Yes | 6 No |
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
To compensate Voltage drop at receiving end
| Is This Answer Correct ? | 42 Yes | 12 No |
Answer / ash
433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.
| Is This Answer Correct ? | 18 Yes | 6 No |
Answer / sagar surve
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / gopalen sv
When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / andy d
It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / percy
433 IS LILNE TO LINE VALUE OF 250
415 IS NOT DIVISIBLE BY 1.732
| Is This Answer Correct ? | 3 Yes | 52 No |
Why should we hire you over the others waiting to be interview?
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
What is meant by unilitrel device?plz tell about h-parametrs
why capacotors burnt out
what is the current law ?
Why capacitor bank is not neccessery to switch on,pls answ me with formula
Why are we not getting shock while touching a metal which is being welded?
why a fan starts rotating in the reverse direction when condenser gets damaged?
Which type of alternator used in power station?
plz send me Bhel, Mahagenco, sbi previous exam paper for electrical engineer on my email-id kambali_smita@yahoo.co.in
How many gap between finger contact in a.c.b. and v.cb.?
what's the simultenous maximum demand (SMD)..what the diffrent MD and SMD?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)