Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why we Specify Transformer rating 433 V Instead of 415V
?

Answers were Sorted based on User's Feedback



Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / n. ramesh

Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.

Is This Answer Correct ?    46 Yes 6 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / n manivannan

Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work

To compensate Voltage drop at receiving end

Is This Answer Correct ?    42 Yes 12 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / ash

433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.

Is This Answer Correct ?    18 Yes 6 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / sagar surve

Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work

Is This Answer Correct ?    15 Yes 9 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / gopalen sv

When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.

Is This Answer Correct ?    3 Yes 2 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / andy d

It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.

Is This Answer Correct ?    1 Yes 1 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / dheeraj

It is a standard

Is This Answer Correct ?    3 Yes 16 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / percy

433 IS LILNE TO LINE VALUE OF 250

415 IS NOT DIVISIBLE BY 1.732

Is This Answer Correct ?    3 Yes 52 No

Post New Answer

More Electrical Engineering Interview Questions

r we are using in gas turbine mark (5) frame (6) (made in india Bhel 1997) &#256;

0 Answers  


HOW TO MEASURE AC VOLTAGE BY USING GALVANOMETER?

1 Answers  


What is meant by Creepage Distance in Insulators?

2 Answers   Areva,


y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..

0 Answers   ME,


In an panel board if the outgoings are power plugs and motor equipments...what should we choose as the incomer of the of the panel board?? MCCB OR ISOLATOR?? Should we use ELCB protection??if so where??

2 Answers  


how does excitation of brushless alternator took place?

1 Answers  


A 3ph load of 10 KW is equal to how many KW of single phase .

1 Answers  


A 60w bulb & a room heater are connected in series.if 60 w bulb is replaced by 100w then what will be the effect on heater out & why?

6 Answers  


What is difference between miniture circuit breaker and module case circuit breaker up to 63Amp.

7 Answers   MSPL,


What is complex power?

1 Answers   DRDO,


why does not tester light up when it is touched to neutral of 3 pin socket.

4 Answers  


What is bushing?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)