Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why we Specify Transformer rating 433 V Instead of 415V
?

Answers were Sorted based on User's Feedback



Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / n. ramesh

Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.

Is This Answer Correct ?    46 Yes 6 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / n manivannan

Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work

To compensate Voltage drop at receiving end

Is This Answer Correct ?    42 Yes 12 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / ash

433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.

Is This Answer Correct ?    18 Yes 6 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / sagar surve

Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work

Is This Answer Correct ?    15 Yes 9 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / gopalen sv

When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.

Is This Answer Correct ?    3 Yes 2 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / andy d

It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.

Is This Answer Correct ?    1 Yes 1 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / dheeraj

It is a standard

Is This Answer Correct ?    3 Yes 16 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / percy

433 IS LILNE TO LINE VALUE OF 250

415 IS NOT DIVISIBLE BY 1.732

Is This Answer Correct ?    3 Yes 52 No

Post New Answer

More Electrical Engineering Interview Questions

why a pilot exciter is used in combination with the main exciter? why not only a main exciter is used for excitation to an alternator?

1 Answers   Electrical,


what is the suitable voltage of transmission line to transmit 10000w power through 250 km. (a)11kv (b)33kv (c)66kv (d)132kv ]and please tell me whats the logic behind it

7 Answers   ONGC,


WHAT HAPPENS IF STARTER OF A FLUROSCENT LAMP IS SHORT CIRCUITED AND WE PUT THE SUPPLY ON?

1 Answers  


what is neutral?

2 Answers  


what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?

0 Answers  


wat is the criteria we use the diff. relay ?

2 Answers  


In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????

0 Answers   Equate,


what is anode and cathode??

5 Answers   Bombardier,


what are the causes for strip heater failure ?

1 Answers  


Difference between control junction box (cjb) and power junction box(pjb)?

0 Answers  


explain working of differential protection for a transformer?

1 Answers   BARC,


WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION?

5 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)