a motor's measured current is 45amp,whereas the rated
current is 38 amps but still it is running ,how?
Answers were Sorted based on User's Feedback
The motor is running due to the non operation of the thermal
over load relay. The motor will keep on running till the
winding temperature increases the designed limit, finally
the motor will burn under the winding short circuit
condition causing production loss & down time .
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rajesh
Ans #1 is partly correct, but probably that is not the
intended answer. Rating of a motor is decided depending on
the ambient temperature. When you say that the rated
current is 38 Amps, what you mean is it can take a
continuous current of 38 Amps at the design ambient
temperature (say 40 degree C). During winter, the ambient
temperature may be 10 deg. At that ambient, it can take a
much higher current. (You can also give extra cooling of
the motor winding by providing an external ventilation
fan).
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sathiarajan
The motor is over loaded. It can work under over load for a
short time period.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sam
ya after the winding overheats it will damage the motor,
the check O/L relay setting and its functioning we had the
same problem.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / hameed
maybe there is a problem in load which this motor run it &I
wender if you cheak all the phases
| Is This Answer Correct ? | 0 Yes | 0 No |
DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
How could a garment factory benefit from renewable energy
how to testing the AC 3 phase motor? and what is the test procedure & kits required for testing?
what is the name for a meter/tester to measure the paint quality in electrical panel or wall?
What will be the effect of in HT XLPE 220 KV cable when one side of the Armour/cable ends are not grounded. Will there is difference between 3-phase voltages? like: if A. Both End of Cable grounded Phase Voltages:- V1=219 KV, v2=220 Kv, v3=220 KV. B. One End is grounded other is not: than Impact on Phase Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or unchanged??
I am getting differential earth fault in my transformer realy , i have checked all its CT & control wiring but do not get fault, Please help
what is the practical application of full adder circuit?
0 Answers College School Exams Tests,
If an electrical component has a positive temperature coefficient, how come such components have high power losses due to heat if current decreases when resistance increases? assuming power given by I^2*R whereby the Resistance is infinite.
what we happen if 400 kvar cpacitor banks are on in manual mode and there is no load on mains ??????????????
what is the circulate the diesel in DG in side pls tell parts name and picture with circulate the diesel
1)Explain why the cradle guard is used on railway crossing in overhead line construction?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)