a motor's measured current is 45amp,whereas the rated
current is 38 amps but still it is running ,how?
Answers were Sorted based on User's Feedback
The motor is running due to the non operation of the thermal
over load relay. The motor will keep on running till the
winding temperature increases the designed limit, finally
the motor will burn under the winding short circuit
condition causing production loss & down time .
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rajesh
Ans #1 is partly correct, but probably that is not the
intended answer. Rating of a motor is decided depending on
the ambient temperature. When you say that the rated
current is 38 Amps, what you mean is it can take a
continuous current of 38 Amps at the design ambient
temperature (say 40 degree C). During winter, the ambient
temperature may be 10 deg. At that ambient, it can take a
much higher current. (You can also give extra cooling of
the motor winding by providing an external ventilation
fan).
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sathiarajan
The motor is over loaded. It can work under over load for a
short time period.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sam
ya after the winding overheats it will damage the motor,
the check O/L relay setting and its functioning we had the
same problem.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / hameed
maybe there is a problem in load which this motor run it &I
wender if you cheak all the phases
| Is This Answer Correct ? | 0 Yes | 0 No |
what do u understand from filter factor of reactor?
what are the difference between protection class CT and Class PS CT
Why is our voltage always seems to be 3.3Kv,11Kv,66Kvetc.. why not 40Kv,39Kv,65Kv???
why after termination of HT cable armoured earth connected one end, why not connect other end.pls tell me correct answer.
why DC is not generated instead of AC?
auto reclosing scheme for radial ehv feeder is to be implemented or not?
How DC earth leakage currents can be reduced ?
how technical is calculated in 11kv line and lt line
How to calculate the cable size in sq. mm. when the load is given in KW?
. Is there a simple method to measure the horsepower of a small motor (1-3 hp) for a non-technical person
Why saturation region slowly shifted in the left side?
what is the load amp of a 2 hp single phase motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)