a motor's measured current is 45amp,whereas the rated
current is 38 amps but still it is running ,how?
Answers were Sorted based on User's Feedback
The motor is running due to the non operation of the thermal
over load relay. The motor will keep on running till the
winding temperature increases the designed limit, finally
the motor will burn under the winding short circuit
condition causing production loss & down time .
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rajesh
Ans #1 is partly correct, but probably that is not the
intended answer. Rating of a motor is decided depending on
the ambient temperature. When you say that the rated
current is 38 Amps, what you mean is it can take a
continuous current of 38 Amps at the design ambient
temperature (say 40 degree C). During winter, the ambient
temperature may be 10 deg. At that ambient, it can take a
much higher current. (You can also give extra cooling of
the motor winding by providing an external ventilation
fan).
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sathiarajan
The motor is over loaded. It can work under over load for a
short time period.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sam
ya after the winding overheats it will damage the motor,
the check O/L relay setting and its functioning we had the
same problem.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / hameed
maybe there is a problem in load which this motor run it &I
wender if you cheak all the phases
| Is This Answer Correct ? | 0 Yes | 0 No |
What is touch potential and step potential?
what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay
1.why ACB is not connected in HT side what Happens? 2.how much voltage maintained in ACB breaker? 3.OLTC is connected in primary side in case secondary side connected what happened?
if we use a normal natural thundering; than approx how much amount of electricity we generate?
What are the components connected in between the power supply coming from an electric pole to HT & LT Panels in a large commercial building or how the power supply connected from Electric pole to Transformer & then to the HT & LT panels of a building? Please send me answers via mail, my id is yogiagarwal@gmail.com. If possible, please give a line diagram.
define regulation
what is the formula for calculate the turns in Transformers
What is different between Difnit time and instatous over current relay
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
What are the steps for Testing of 6.6KV HT Panels?
importance of air gap in transformer
Dyn1 transformer vector group testing how to do
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)