a motor's measured current is 45amp,whereas the rated
current is 38 amps but still it is running ,how?
Answers were Sorted based on User's Feedback
The motor is running due to the non operation of the thermal
over load relay. The motor will keep on running till the
winding temperature increases the designed limit, finally
the motor will burn under the winding short circuit
condition causing production loss & down time .
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rajesh
Ans #1 is partly correct, but probably that is not the
intended answer. Rating of a motor is decided depending on
the ambient temperature. When you say that the rated
current is 38 Amps, what you mean is it can take a
continuous current of 38 Amps at the design ambient
temperature (say 40 degree C). During winter, the ambient
temperature may be 10 deg. At that ambient, it can take a
much higher current. (You can also give extra cooling of
the motor winding by providing an external ventilation
fan).
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sathiarajan
The motor is over loaded. It can work under over load for a
short time period.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sam
ya after the winding overheats it will damage the motor,
the check O/L relay setting and its functioning we had the
same problem.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / hameed
maybe there is a problem in load which this motor run it &I
wender if you cheak all the phases
| Is This Answer Correct ? | 0 Yes | 0 No |
Give 3 phase transformer connections for 24 pulse rectifier using thyristors.
What should be the minimum and maximum ohmic value for earthing?
what is meant by damper winding ?
how you taken aotitude test
how invertor convert the dc into ac give brif detail
Why we use parllel operation of alternator
how we calculate electrical load on a building according to area?
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
18 Answers Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
in wind mill use 2100 kw asychronous generator ( induction generator ) rotor voltage : 3300,stator voltage : 690, rpm : 1511 type : MRL063E04 ' we check rotor resistance magger value found following. R-EARTH - 00 M.OHM,Y-EARTH-34 M.OHM,B-EARTH- 33M.OHM R-Y: 31 M.OHM, Y-B: 00 M.OHM,B-R :33 M.OHM HOW CAN I TAKE DECISION?pls ans. quickly
what is the specific gravity of fully charged battery
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)