what is the effect of power factor in electrical circuit ?
if we mainten power factor near about unity (0.999) our
energy consumption Units increase or decrease?
Answers were Sorted based on User's Feedback
Answer / yogesh
As we know Load is in KW & it is constant. PF will not
change units consumed as we are measuring energy consumption
units in KW not in KVA, only transmission losses will be
reduced.
KW=1.73 X V X I X cos phi
AS KW is constant, voltage is constant if cos phi changes
current will be changed.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / b chaudhary
Power facotor does not effect on energy consumption.But
transmission and distribution losses can be reduced.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rahul verma
Electrical energy is exclusively
generated,transmitted,distributed in the form of
alternating current.therefore the question of power factor
immediately comes in to picture.since most of the loads are
inductive in nature hence have low lagging pf.low pf is
highly undesirable as it causes increase in current,and
additional losses of active power in all the elements from
power station generation till the utilization devices.
if we maintain pf as close to unityour consumption unit
decrease
| Is This Answer Correct ? | 13 Yes | 8 No |
with power factor at unity the power consumption will not
get effected . but for sure the production cost will
decrease with which the cost of consumption will decrease.
and how the production cost will decrease???
answer is with unity pf the real power will be v*i*cos@=v*i
which is actuall input power and now is usefull power.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / santosh kawade
Electrical energy is exclusively
generated,transmitted,distributed in the form of
alternating current.therefore the question of power factor
immediately comes in to picture.since most of the loads are
inductive in nature hence have low lagging pf.low pf is
highly undesirable as it causes increase in current,and
additional losses of active power in all the elements from
power station generation till the utilization devices.
If we maintain pf as close to unity transmission losses
reduces but our consumption units will not change.
santosh kawade
9224693116
| Is This Answer Correct ? | 3 Yes | 1 No |
if power factor lagging then losses will increase, then more
units will consumption.pf should not in leading position.so
to reduce that losses we ll maintain pf close to unity....if
pf is 1 then we ll get kva=kw....reading...THEN UNITS WILL
GET REDUCE,....
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sumedh chaccravorty
The units consumed will NOT change but the company might( most probably will) impose punishments for operating at lower PF as it increases the transmission losses and increases the KVA rating of the associated devices.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / parasuram
effect of power factor in eleectrical circuit is if power
factor is very less reactive power wwill be more it will
cause to damage circuit and energy consumption units
increase.
if power factor is near to unity it will decrease the enegy
cosumption units.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / suraj ojha
As per power fourmula :-
1.Unit cosumption will raise for consumer.
2.Unit generation will increase for genarating station.
| Is This Answer Correct ? | 1 Yes | 5 No |
What is broken wire condition in transmission line?
Why does the phase voltage of two healthy phases become equal to the line voltage in case of an ungrounded neutral 3 phase star connected sytem when a single line to ground fault occurs ?
why supervision relay is used in incoming feeders?
what is consequences of neutral and earth connect?
how many earthing required for ups, what should be the earth voltages
How many battery required for an 3kva online ups with 3 hrs back up with usage of 3 fans,3tube lights
Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted
What is dynamo?How it works and what is the function of dynamo in a DG.
what type of earthing is done on hilly rocks.
why transformer rating comes in kva?
What is advantages of ungrounded neutral?
in a solar power plant,we are going to step up the voltage 350V to 33kv, and to 132kv GSS. i want to ask that if it is possible that 315v/33kv is not possible because we also use 315v/11kv. or it should be 415v/33kv? is it effects generation or losses? the second question is-generation is depends on LV winding? or LV winding design for generation voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)