Why tripping not occur when the transmission lines (11KV &
above) breaks? Doesn't
we provide earthfault protection for it?
All the tr lines should be provided with EF protection.11
and 33 KV lines are provided with 2 OC and 1 EF relays or 3
OCR and 1 EFR.The unbalanced current passes through the EFR
which is usually set at 20% of OCR setting.The EFR is
connected between star points of CT's and relays. For
higher voltages distance relays are provided with OCR and
EFR as back up protection.If the line breaks i.e.a
conductor opens out without touching earth .The distance
relay does not act as there is no heavy current.The EFR
will trip only if the unbalanced current exceeds the set
value .Hence there will not be any tripping if the line is
not loaded sufficiently. OCR=over current relay, EFR =earth
fault relay
Is This Answer Correct ? | 5 Yes | 0 No |
What it is the diff btw Package & PEC AC's????
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
How to write a progrramme to turn ON and turn OFF a motor with a single push button in AB?
2 Answers HCL, Torrent Pharma,
effect of single phase transformer on full load current?
If the ceiling fan is on slow speed, does it consume less electricity?
what are the different types of bus bar used at electrical work at shelter
3 Answers Aster Teleservices, Costco,
motor work in hat principle generator work in what principle transformer work in what principle pls explain with details or answered to ramadoss.sepc@gmail.com
what is the function of a Master trip relay? why is it used ?
5 Answers ABB, Nissi Engineering Solution,
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
what purpose of the percentage impendance in transformer
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
what's the outstanding feature of universal motor?