How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
Answer / abdul rahman
Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC
Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor
So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.
| Is This Answer Correct ? | 4 Yes | 0 No |
what is cogging and crawling
what is the ground clearance of 400KV transmission line?
9 Answers Power Grid, wbsedcl,
What are your personal skills and abilities for such a Master Course and your possible preparation to undertake this course?
what is the reason for balance of voltage in magnetic balance test?
what is current check gurd relay?
what will be the difference on output when 3phase I.M. is given a delta or star supply?
what are the specifications we must look at to select a relay for any capacity motor?
What is stray looses?
why all the feeders are designed in a particular manner ... is there any reason for that???
What does impedance in the windings of transformer signify.
why can we use cosine wave instead of sine in ac supply as both have same rms vale and ripple factor
0 Answers Indcoil Transformers, Power Grid,
what should be the motor rating for pumping water for house hold use from 60km far lake and what formula is to use please tell me
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)