How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
Answer / abdul rahman
Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC
Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor
So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.
Is This Answer Correct ? | 4 Yes | 0 No |
what is surge suppressor?
As we know multiplicity factor derivation equation is as below MF = main c t ratio / main p t ratio * meter c t ratio / meter p t ratio * meter dial constant Where in digital meters for HT kwh import export now a days meter constant are calibrated already which is 1 So my question is For HT 11kv 110 v line values are as below Main c t and p t ratio are 11000 v and 110 v and 20/5 means 20 amp and 5 amp Now meter values are 11000/√3/110√3 and primary and secondary amp are displayed as -/5 amp on kwh meter so what will be the MF for this meter ?
what is the difference between RMS & TRUE RMS VOLTAGE
how we can to the synchronization in transformer. What are the conditions for that.
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
Ps Explain YWY,AFWY Type Cable
Define what is difference between fuse and breaker?
what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?
Can we use 1.1x 2 split air-conditioning at a same time in 2kw power loadar
I had attend the ITC (Indian Tobacco Company) interview (For Electrical maintanance).There they was conducted me a written test.And I was passed in that.Now They are going to conduct a Practical Interview in next round.Please help me what practical test they will ask............?
what is integrated ac contact circuit
Wat is power factor exact meaning in terms of technical terms plz explain ?