Answer / abdul rahman
Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC
Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor
So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.
| Is This Answer Correct ? | 4 Yes | 0 No |
how tto ingress mw in turbine explain.procedure ?
plz send me the syllabus or any sample paper for engineer trainee recruitment if any,on ravinder911@yahoo.com
0 Answers Bhel, Maruti Suzuki,
what is earthed and inearthed cable or system?
what types of cable used in underground coal mining?
Name the instruments which run on DC?
Why neutral grounding Transformer provided for generator?
Which type of transformer used in lighting load?
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
what is the value of current as well as voltage upto which we will not feel shock and why?
why we store only dc in batteries ?
why transmission lines traveled in high voltage?
how the reverse power relay acts..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)