How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
Answer / abdul rahman
Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC
Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor
So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.
| Is This Answer Correct ? | 4 Yes | 0 No |
If not into production, how far did you follow the design and why did not you see it into production?
0 Answers Bharti, Havells, Intel,
our factory is going under construction mean time transformer 1000 kva 2 nos &load break swithch 12 kv & 4 nos 750 kva 2 nos & 380 kva 2 nos generator to be errcted.how to arrange earth pits &how to earth connect & neutral pit how to calculate in earth bit size.
In 11kv transmission line whats the maximum power can be drawn?
I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?
my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.
what deffrence between KW $ KVA ?
How to determine the Power factor is Leading,Lagging & Unity ?.I don'thave any Meters.
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
WHAT ARE THE EFFECTS OF SERIES RESONANCE AND PARALLEL RESONANCE ON THE CIRCUITS PARAMETERS?
How to select the different contactors ( starter combination) for different AC motors? what about fuse cappacity 4 different motors too?
where we take earth in hill station
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)