Answer / yashpal
plug setting is = 3.75 means pick up= 3.75 A.Relay
operating time will depends on the charecteristic of relay.
(invese,normal inverse).if the fault current is 8000A then
current in the sec will be 10 A which is three times of
3.75A(connected plug setting),now just watch the relay
charteristic written on relay u can get the time required
for relay operation.(ex- for inverse charecteristic relay
for 3 time current & tms = 1 ,timing is 6.25 sec,so for
our problem timing will be 6.25 * 0.15=0.9375 sec.
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / yvb
your PSM set for 3.75 means 3.75 times of your py.
current. if fault current is 3.75 times of 4000 i.e 3.75 x
4000 = 15000 A. your relay will operate in 0.15 sec.(
Primary Injection.)on Secondary we can say 5 x 3.75 =
18.75A flows through ur relay.
Now comming to ur case if fault current is 8000A ie. 2
times of 4000 or u can say 2 times of 5 A.
Then your relay will operate in 0.282 seconds.
| Is This Answer Correct ? | 6 Yes | 10 No |
IF we have 500kva transformer & know the current on HT & LT side, how can we consider for its breaker?
What is the theoretical capacity of a channel in each of the following cases? i) Bandwidth: 20KHz SNR(dB) =40 ii) Bandwidth: 200KHz SNR(dB) =06 iii) Bandwidth: 1MHz SNR(dB) =20
What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)
17 Answers Alstom, Call Centre, EDC, HCL, Procon Engineers,
if the field circuit of a d.c. shunt motor running without load gets opened, then the motor will
Graphs of measuring power and speed on dc motor
how to maintain ht line?
WORKING PRINCIPAL OF MCB
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?
How many no of flip-flops are required to get 16 bit counter
Our Alternator nameplate specifies a power factor of 0.8. When the Alternator is on light load, the bus bar voltage rises to 11240 volts, whereas the standard value is 10500 volts. Is it ok to increase the power factor to 0.85 or 0.9. I am afraid because the power factor on the name plate is only 0.8 ?
how the capacitance is caluclated if the load is varying to keep the power factor constant(above0.95)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)