plz explain TSM and PSM.with example suppose ct ratio is
4000/5 and tsm is .15 and plug is at 3.75 if fault current
is 8000A.so how i find relay oprating time.
Answers were Sorted based on User's Feedback
Answer / yashpal
plug setting is = 3.75 means pick up= 3.75 A.Relay
operating time will depends on the charecteristic of relay.
(invese,normal inverse).if the fault current is 8000A then
current in the sec will be 10 A which is three times of
3.75A(connected plug setting),now just watch the relay
charteristic written on relay u can get the time required
for relay operation.(ex- for inverse charecteristic relay
for 3 time current & tms = 1 ,timing is 6.25 sec,so for
our problem timing will be 6.25 * 0.15=0.9375 sec.
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / yvb
your PSM set for 3.75 means 3.75 times of your py.
current. if fault current is 3.75 times of 4000 i.e 3.75 x
4000 = 15000 A. your relay will operate in 0.15 sec.(
Primary Injection.)on Secondary we can say 5 x 3.75 =
18.75A flows through ur relay.
Now comming to ur case if fault current is 8000A ie. 2
times of 4000 or u can say 2 times of 5 A.
Then your relay will operate in 0.282 seconds.
Is This Answer Correct ? | 6 Yes | 10 No |
What is the difference between ACB & MCCB?
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
i want to put single phase load on scott connected transformer,eventhough how to balance the transformer.
what is the difference between kva and kw ?
how can we test the vector group of transformer
Hi, what is the temp of bus bar.
How is the Depth of Stator Slot being calculated for Synchronous Generator?
What are the types of Bus bar?
what is the difference betweem star connected motor & delta connected motor?
How to calculate 33 kv panther conductor line losses.
1 Answers Construction, Orange,
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
How much earthing require for h.t.22 k.v. cable in coming side & out going & 22 lighting arrest or,22 k.v.D.o. & A.B. switch.