125Kva Dg can take up how much amphere load.
Answers were Sorted based on User's Feedback
Answer / debaraj das
125 KVA DG = 174A ( In 100% Load)
80% Load of 125 KVA DG = 140 A
( 80% is the Safer load you can give to your DG Set)
| Is This Answer Correct ? | 63 Yes | 6 No |
Answer / guest
V= 415
KVA = 125
A = KAV/V*Root3
= 125/415*1.732
= 173.905 Per Phase
| Is This Answer Correct ? | 54 Yes | 12 No |
Answer / rajesh
The best answer is 125 Amps.
Normally the best operation is carried at 80% of load.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / shridhar awasthi
125 kva dg will take 173.90 amps on 100% loading and 191.29
amps at 10% over loading according to I=KVA/sqrt3*voltage
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / nadhan
Why should not we add the capacitor bank for dg set alternator to minimize the dgset load current.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sk aminul hossain
Amp=kva*p.f/volt*root3 So
125*1000*0.85/415*1.732 (k=1000,v=415,p.f=0.85) reactive power
So, amper=147.81A or 148A
| Is This Answer Correct ? | 1 Yes | 1 No |
-----------means a source which can supply a constant voltage to aload irrespective of the valu of load resistance.
Is there any scope for an electrical engineer in MRF company......
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
how calculate gd2 of ht motors
4 Answers Hindustan Copper Limited, Kohler India,
wheather the size of windings in motor and generator are the same
Why negative feedback is preferred in the control system?
why PD testing for power cables
1 Answers Bhushan Power Steel, CSE, Datre Corporation,
How can maintain our H.T. motors used in cement plant. please send me procedure.
What is a HRC fuse (Full form)
26 Answers Gammon, HRC, Moser Baer,
Mention the difference between Analogue and Digital circuit?
EXPLAIN WHY THE SURGE CURRENT RATING OF AN MCCB OR CIRCUIT BREAKER DECREASES WITH INCREASE IN THE RATING OF MCCB OR CIRCUIT BREAKER.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)