125Kva Dg can take up how much amphere load.
Answers were Sorted based on User's Feedback
Answer / debaraj das
125 KVA DG = 174A ( In 100% Load)
80% Load of 125 KVA DG = 140 A
( 80% is the Safer load you can give to your DG Set)
| Is This Answer Correct ? | 63 Yes | 6 No |
Answer / guest
V= 415
KVA = 125
A = KAV/V*Root3
= 125/415*1.732
= 173.905 Per Phase
| Is This Answer Correct ? | 54 Yes | 12 No |
Answer / rajesh
The best answer is 125 Amps.
Normally the best operation is carried at 80% of load.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / shridhar awasthi
125 kva dg will take 173.90 amps on 100% loading and 191.29
amps at 10% over loading according to I=KVA/sqrt3*voltage
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / nadhan
Why should not we add the capacitor bank for dg set alternator to minimize the dgset load current.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sk aminul hossain
Amp=kva*p.f/volt*root3 So
125*1000*0.85/415*1.732 (k=1000,v=415,p.f=0.85) reactive power
So, amper=147.81A or 148A
| Is This Answer Correct ? | 1 Yes | 1 No |
2. What are the parameters of EHT sub-station?
1 Answers APGenco, Blue Star, Enercon,
what is the dedicated neutral earth in ups? y its required?
how do you measure earth leakages in 3phase wires?
Any Electrical Engineering jobs?Please refer for interviews. Thank you
how to reduce earth resistance in sandy soil.
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
iam working as a electrical engineer. i want to know about any license or certificates regarding my field. for my carrier and ti improve the knoweledge.,,, how we get that..and what procedures......... pls help me
what is the abbreviation for F.M In FM-200 fire suppression system
Fault current shall be part of tech specs of power cable or not?.
why we are caling 440 volt 3 phase supply instead of 660 volt 3 phase supply? because each phase as a voltage of 220 volt. if anybody know the answer for my question please send it to my mail id. thank you.
3 Answers College School Exams Tests, Jindal Steel and Power, JIOL, NEC,
how could we know the size of cable by physical view?
1 Answers Havells, United Engineering,
Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc........
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)