Answer / pillay
i assume your question is how to take transformer oil for
breakdown voltage test.
the sample is taken from the oil drain cork. the containers
and any other equipment used for this job must be ensured it
is dry and not contaminated or this contamination will
influence the oil test results.
1. The sample is connected from the drain cork through a
small hose to a syringe. the initial oil is not taken. from
the syringe the oil is transfered to a sample bottle slowly
without forming air bubbles or too much external atmospheric
contact.this oil is used to test for the dielectic breakdown
voltage in a special tester.the minimum breakdown voltage
depends on the operating systems voltage and local
regulations.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shaikh
Hi Pillay! can you explain why initial sample of oil is not
taken and what amount of oil is requied for testing?
| Is This Answer Correct ? | 0 Yes | 0 No |
What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??
why do we have spikes enough to burn electronic boards, when generators are not grounded
why the difference arise between HT reading & LT reading (submeters fixed in complexes, apartments etc)if the power factos exceed from 0.9 to 1 can the ht meter reads fast?
how do you find making current and breaking current of the circuit breaker
what happen ehen synchronisation is done at below rated speed
why ct secondary side shortlink provided? its open what will happen?while running ?
what is ohms law?
100V supply is appllied between 500K Resistance bulb. for 1 kwh energy, how long time the bulb will glow? explain the calculating method.
We know that primary transmission is done to reduce current so that i^2*r loss could be minimised but according to ohm's law v is directly proportional to i,which indirectly means higher potential difference means larger current?so how the current is minimised in high power transmission line??
What is EHT tariff or Power factor Tariff ????
why the supply power frequency is 50hz in india? where as it is 60hz in US?
in wind mill use 2100 kw asychronous generator ( induction generator ) rotor voltage : 3300,stator voltage : 690, rpm : 1511 type : MRL063E04 ' we check rotor resistance magger value found following. R-EARTH - 00 M.OHM,Y-EARTH-34 M.OHM,B-EARTH- 33M.OHM R-Y: 31 M.OHM, Y-B: 00 M.OHM,B-R :33 M.OHM HOW CAN I TAKE DECISION?pls ans. quickly
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)