how much Amp we can put in 1200kva generator?
Answers were Sorted based on User's Feedback
Answer / mohamed ali
Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8
100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mohamed ali.m
Dear there are use the Formula
I= KVA X 1000/1.732 X 415
For Example
1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / deepak tyagi
KVAX1000= 440XIX1.732
I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijay
hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijayakrishnan
KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nikhil shinde
assume, pf=0.8
then
1200*0.8=960 KVA
I=kw*10^3/1.732*v
=1335.55 @100%
=1068.44 @80%
| Is This Answer Correct ? | 0 Yes | 2 No |
Why let through energy not considered for ACB breaker while cable sizing?
Why we check only first column of root locus..?
Wt is the function of reactive power? How it generates & consume though resultant is zero?
how are reversing the direction of dc motor
On a transformer name plate %IZ(%Impedence) is mentioned. What is the meaning of %IZ and how it is calculated?
3 Answers Ambe Consultancy, Siemens,
What are the parameters of water ( Water quality )to be monitored in Centralised HVAC ( water cooler chillers )
Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?
Explain using drawings what is reverse PID action w.r.t PID controllers.
What are the types of piano switches?
In a star-star connected h.t transformer why we use NGR on the secondary (l.t)side.
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
how the testing of CT OF 400/200/100 done in33/11 kv s/s
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)