Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much Amp we can put in 1200kva generator?

Answers were Sorted based on User's Feedback



how much Amp we can put in 1200kva generator?..

Answer / kumar

as per my field knowledge by using formula
I= KVA X 1000/1.732 X 440 X 0.8

THERFORE ANSWER IS :1694A

Is This Answer Correct ?    14 Yes 2 No

how much Amp we can put in 1200kva generator?..

Answer / mohamed ali

Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8

100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps

Is This Answer Correct ?    8 Yes 0 No

how much Amp we can put in 1200kva generator?..

Answer / mohamed ali.m

Dear there are use the Formula
I= KVA X 1000/1.732 X 415

For Example

1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)

Is This Answer Correct ?    6 Yes 0 No

how much Amp we can put in 1200kva generator?..

Answer / a.bala

As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A

Is This Answer Correct ?    5 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / soma

AS SAME

Is This Answer Correct ?    2 Yes 2 No

how much Amp we can put in 1200kva generator?..

Answer / thran

1668 exactly amps rating!

Is This Answer Correct ?    0 Yes 0 No

how much Amp we can put in 1200kva generator?..

Answer / deepak tyagi

KVAX1000= 440XIX1.732

I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.

Is This Answer Correct ?    0 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / vijay

hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf

Is This Answer Correct ?    0 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / vijayakrishnan

KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only

Is This Answer Correct ?    0 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / nikhil shinde

assume, pf=0.8
then
1200*0.8=960 KVA

I=kw*10^3/1.732*v

=1335.55 @100%
=1068.44 @80%

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is the capacitance of a single conductor

6 Answers   Bhel,


LT cable fault checking instrument is available? where and how to get it.

2 Answers  


how to do the ductor test?

0 Answers  


what is your majour contributions in your present job

0 Answers   ESL,


i want to measure voltage difference between neutral and earth so i just simply use voltmeter. my question is that may i use this measure continuosly.or there are some electricity board restrication on that? or it creat some problem on my measuring device..?

2 Answers   NEEC,


could anyone suggest project title

1 Answers   Engineering,


what is the practical application of full adder circuit?

0 Answers   College School Exams Tests,


what will happen if field winding supply of synch generator accidently got disconnected?

4 Answers  


What is knee point voltage?

0 Answers  


what is the meaning of the symbol << >> put in transformer drawing

0 Answers   TATA,


how to select short circuit current while selecting a MCCB? how to calculate current for a given KVA and KW load?

2 Answers   GE, PnU Engineering,


how we can come to know that motor winding resistance which showing by DMM is right or wrong???is there any chart or something that we will compare & check???

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)