Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much Amp we can put in 1200kva generator?

Answers were Sorted based on User's Feedback



how much Amp we can put in 1200kva generator?..

Answer / kumar

as per my field knowledge by using formula
I= KVA X 1000/1.732 X 440 X 0.8

THERFORE ANSWER IS :1694A

Is This Answer Correct ?    14 Yes 2 No

how much Amp we can put in 1200kva generator?..

Answer / mohamed ali

Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8

100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps

Is This Answer Correct ?    8 Yes 0 No

how much Amp we can put in 1200kva generator?..

Answer / mohamed ali.m

Dear there are use the Formula
I= KVA X 1000/1.732 X 415

For Example

1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)

Is This Answer Correct ?    6 Yes 0 No

how much Amp we can put in 1200kva generator?..

Answer / a.bala

As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A

Is This Answer Correct ?    5 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / soma

AS SAME

Is This Answer Correct ?    2 Yes 2 No

how much Amp we can put in 1200kva generator?..

Answer / thran

1668 exactly amps rating!

Is This Answer Correct ?    0 Yes 0 No

how much Amp we can put in 1200kva generator?..

Answer / deepak tyagi

KVAX1000= 440XIX1.732

I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.

Is This Answer Correct ?    0 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / vijay

hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf

Is This Answer Correct ?    0 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / vijayakrishnan

KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only

Is This Answer Correct ?    0 Yes 1 No

how much Amp we can put in 1200kva generator?..

Answer / nikhil shinde

assume, pf=0.8
then
1200*0.8=960 KVA

I=kw*10^3/1.732*v

=1335.55 @100%
=1068.44 @80%

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

2. What are the parameters of EHT sub-station?

0 Answers   APGenco,


6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200 Amp. Would there be any effect on performance of ACB due to lower voltage rating?

5 Answers  


DG drop how much freqency at 100% load?

3 Answers  


Is it possible to measure the voltage of a battery from a single terminal?

0 Answers  


what is the full form of ka (100A mccb KA)

1 Answers  


i am working in a grid substation,TNEB having 13 yrs experience. Am I eligble to get apply for c licence now?

3 Answers  


Whats the purpose of neutral earthing?

5 Answers   Electrical, Hindalco, TCS,


Name one of major transformer company in KSA ?

0 Answers  


What is the difference between KV,KVAR,KVA,KW?

6 Answers   L&T, PowerHouse, YUI,


wat will be the pressure maintained inside the transformer?

2 Answers  


how to carried out DAR test in 11 KV Alternator ?

0 Answers  


If DC supply is given to a transformer it may a) Work b)Not Work c)Give lower voltage than the rated voltage on secondary side. d)burn the winding

12 Answers   wbsedcl,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)