how much Amp we can put in 1200kva generator?
Answers were Sorted based on User's Feedback
Answer / mohamed ali
Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8
100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mohamed ali.m
Dear there are use the Formula
I= KVA X 1000/1.732 X 415
For Example
1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / deepak tyagi
KVAX1000= 440XIX1.732
I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijay
hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijayakrishnan
KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nikhil shinde
assume, pf=0.8
then
1200*0.8=960 KVA
I=kw*10^3/1.732*v
=1335.55 @100%
=1068.44 @80%
| Is This Answer Correct ? | 0 Yes | 2 No |
HOW DG WORKS ?
What is Grounding? any difference b\w earthing? if yes plz explan??
how can i get an electrical c-certificate?
description with working of all parts of a Diesel generator???????
What is slip in induction motor?
in the thermal power plant, why we use the condenser (for cooling the steam) when we have to heat the steam again. i mean why we are cooling the steam,
What is Automatic interlocking circuit dighram between two contactor for DG SET panel.
why the LED of my electrical meter glows even after the line has gone. what actually the reason?
why should we connect the no load components in a equivalent circuit of transformer in parallel?why cant it be in series.
what is current
53 Answers Bio Enterprises, CLG, TCS,
Hi My Dear All Friends, There is one question it is widely used in Power Project's High Voltage Engineering. Question- What is the diffrence between Earth fault and Back up Earth Fault....???? . . . . . . Have A Good Day
Actually why the transformers are rated in KVA.?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)