how much Amp we can put in 1200kva generator?
Answers were Sorted based on User's Feedback
Answer / mohamed ali
Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8
100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mohamed ali.m
Dear there are use the Formula
I= KVA X 1000/1.732 X 415
For Example
1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / deepak tyagi
KVAX1000= 440XIX1.732
I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijay
hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijayakrishnan
KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nikhil shinde
assume, pf=0.8
then
1200*0.8=960 KVA
I=kw*10^3/1.732*v
=1335.55 @100%
=1068.44 @80%
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the capacitance of a single conductor
LT cable fault checking instrument is available? where and how to get it.
how to do the ductor test?
what is your majour contributions in your present job
i want to measure voltage difference between neutral and earth so i just simply use voltmeter. my question is that may i use this measure continuosly.or there are some electricity board restrication on that? or it creat some problem on my measuring device..?
could anyone suggest project title
what is the practical application of full adder circuit?
0 Answers College School Exams Tests,
what will happen if field winding supply of synch generator accidently got disconnected?
What is knee point voltage?
what is the meaning of the symbol << >> put in transformer drawing
how to select short circuit current while selecting a MCCB? how to calculate current for a given KVA and KW load?
2 Answers GE, PnU Engineering,
how we can come to know that motor winding resistance which showing by DMM is right or wrong???is there any chart or something that we will compare & check???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)