how the testing of CT OF 400/200/100 done in33/11 kv s/s
actually the ct used in ss is in the range of 400-200-
100/1A.THE MAIN TESTS CONDUCTED ON CT'S ARE TWO 1.IR VALUES
FINDING TEST AND 2.RATIO TEST
1.IR VALUES ARE FINDING THROUGH 0.5,1,2.5,5KV STEPPED
MEGGER.GENERALLY IN APTRANSCO USES MOTARISED RIKEN MAKE
MEGGER.
2.RATIO TEST CAN BE CALCULATED BY PRIMARY CURRENT INJUCTION
KIT.
AND THE 3. GENERAL TEST IS POLARITY TEST.
Is This Answer Correct ? | 8 Yes | 0 No |
what is meant by k-rating in isolation transformer?what is k9, k14 stands for?
1.WHAT IS A SMART CAPABLE DB ( DISTRIBUTION BOX) ? 2. HOW TO DECIDE THE TYPE OF DB TO BE USED ( RECESSED/ PLUG TYPE/ SMART ETC ETC? 3. WHAT IS MILLENEUM BUS BAR USED IN DB? 4.DIFFERENTIATE MCCB AND MCB.
difference between generator and alternator
why to use freewheeling diode ( diode in revers bias mode) across dc coil
my company total load is 1000kw, 415volt, all load are inductive load. incoming powerfactor is .8. we want to have0.95 pf connecting capacitors. so now how much rating of capacitors we have to connect? show how?
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
what is difference between DC and Ac
what is the differences between microprocessor and general purpose computer
What is the difference between short circuit and overload currents?
We wish to test 60 Hz systems from a 50 Hz supply. To acheive frequency conversion, we use a VFD. The VFD powers 40 kVA transformer, which has motor and non-motor loads on it. Will the transformer work?
how to calculate short circuit breaking capacity KA for 2500kva 33kv transformer.
If two induction motors A and B are identical except that the air-gap motor 'A' is 50 % greater than that of motor 'B', then