how the testing of CT OF 400/200/100 done in33/11 kv s/s
actually the ct used in ss is in the range of 400-200-
100/1A.THE MAIN TESTS CONDUCTED ON CT'S ARE TWO 1.IR VALUES
FINDING TEST AND 2.RATIO TEST
1.IR VALUES ARE FINDING THROUGH 0.5,1,2.5,5KV STEPPED
MEGGER.GENERALLY IN APTRANSCO USES MOTARISED RIKEN MAKE
MEGGER.
2.RATIO TEST CAN BE CALCULATED BY PRIMARY CURRENT INJUCTION
KIT.
AND THE 3. GENERAL TEST IS POLARITY TEST.
| Is This Answer Correct ? | 8 Yes | 0 No |
what is FACTS & where i can material regarding to facts.
why we are testing cables with DC supply not with AC supply?
9 Answers Aurobindo, DEWA, L&T,
what are the C&D CHECK OF DG set
why ie corona losses in tranmission line
How do you protect your appliances from harm in case of neutral failure in a three phase power supply set up.
Merits & Demarits of Oil circuit & Air circuit breakers ?
what is the difference between earth and neutral?
56 Answers Bhel, Emerson, HCL, JLL, L&T, Siemens, TVS,
What is the function of Antipumping Relay and Lockout Relay?
(1) From the following option, which option is correct for largest size transformer.? a)1KVA,25Hz , b)1KVA,50HZ , c)1KVA,60Hz , d)1KVA,100Hz
How to prepare electrical preventive maintenance plan & shedule of machine tools in manufacturing unit.
While connecting bulb in Series/Parallel,there is any difference in glowing
how to calculate the kw, Amps consumed by a capacitor, give me the formula for KVAr into capacitance,KVAr into KW & KVA, Amps
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)