in the pipe line if the control valve fails to respond to
controller action,by what means we can stop the flow in the
pipe line ?
Answers were Sorted based on User's Feedback
Answer / renjith
For every control valve there will be option to manually
close the valve by adjusting a screw.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / priya sharma
u can stop the air supply with the control valve accessory
that is the AIR LOCK
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / nilmaheshin@yahoo.co.in....jit
Chitanya wrote correct answer. Priya and renjith are also
correct. But dear when any body is not present in field at
that time fail safe action is responding
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / karthikeyan
absolutely right answers(1&2)....we can operate in manually,and also to remove the air line because feed water control valve should be a air to open,in this if air fail it should be close....
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashwin jain
but wat happen if no 1 is there to control
manually..chetanya's answer is correct....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mrmk
Good Suggestion.But if a control valve fail to operate
there may be so many reason.In practical,If you want to
isolate/stop the flow immediately it can be done easily by
closing upstream isolation valve.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / deepak
if something stuck in control valve then what will u do??
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the difference between Pressure Safety Valve and Pressure Relieve Valve, in what condition we prefer choose Pressure Safety Valve rather than Pressure Relieve Valve? and vice versa
.==PL..PL.. FORWARD TO MANAGER PURCHASE./ / Q.ASSU. DEPT.. =FROM==AJAY ENTERPRISES ===============PUNECITY..INDIA. DEAR SIRS,............. ======================================================== =NEW SUPPLY/ REPAIRING AND CALIBRATION =OF=MECHANICAL /DIGITAL / ELECTRONIC=PRECISION MEASURING INSTRUMENTS=FROM == 22YEARS. ============================================================ = 1.==NAME OF THE COMPANY= AJAY ENTERPRISES 2.=ADDRESS OF THE COMPANY= OFFICE NO 08, DALAL CHAMBERS, MKTYARD PUNE= 411037. ===== TEL- 020 242601! 09. MOB- 0 98900 98941. 3.=EMAIL= ajaygujar1@gmail.com.-- AND-- ajayenterprises1@yahoo.com--- =========================================================== 4.=ACTIVITY OF THE COMPANY= SUPPLIER OF PRECISION MEASURING INST RUMENTS AND MAGNETIC TOOLS IN PUNE== [ MITUTOYO / TESA / KUMAUN / MAHR / BRITOOL / TOHNICHY / DIATEST-GERMANY / IMADA / TECKLOK / SYLVAC /ADITYA=ACCURATE / BAKER/ CRYSTAL / FLUKE-RAYTEK ETC. 5.=SUPPLY= VERNIER CALIPERS / MICROMETERS / HEIGHTGAUGES / SLIPGAGE / BORE DIAL GAUGES / MEASURING PINS / TORQUE WRENCHES / GAUGES.. PLUGGAUGES / RINGGAUGES / SHORE A / D HARDNESS TESTERS / DIAL THICKNESS GAUGE / FEELER GAUGES / ELECTRONIC COMPARATORS WITH PROBES / DFTMETERS / SURFACE ROUGHNESS TESTERS / DIGITAL= COATING THICKNESS METERS / PROFILE PROJECTORS /.. WE ARE ALSO DEAL IN == DIGITAL TACHOMETERS / =MULTIMETERS! / VIBRATION METERS / MEGERS- INSULATION METERS / =TE! MPRATURE INDICATORS / SOUND-LEVEL METERS / ETC... =AGENCY- FLUKE- RAYTEK.. MECO....LUTRON...KYORITSU....RION... ..................KELIEWS......AND MANY MORE ===AJAY GUJAR ...AJAY ENTERPRISES =08 DALAL CHAMBERS MKTYARD ROAD NEAR NISARG KARYALAYA =MARKETYARD PUNE= 411037.. =TEL= 020 2426 0109. =MOB=09890098941. =EMAIL=AJAY.MITUTOYO@GMAIL.COM =WEB--WWW.GUJARWORLD.COM
what is diff between sensors and transducers.explain with ex?
what do u mean by compensation n pid tunning?in pid tunning what you tunned?is it possible 2 tune p i d
How to work ultrasonic flow meter ?
Can be operate control valve without positioning if yes ? how and why?
how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp side?
WHAT IS INSTRUMENTATION?
In electronic board one fuse(rating 230v,100ma)showing 2.5 ohms with multimeter,then the fuse is healthy or not.
Differentiate between PLC, SCADA and DCS systems
1 Answers Mumias Sugar, SRF, Trimula Industries,
can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?
how to calibrate bubbler type level transmitter of rosemount make and how to set air flow according to the range.. give one calibration procedure with one example
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)