A bubbler system uses a pneumatic differential relay as a constant flow regulator. Most bubbler systems include a variable area flowmeter, a rotameter, to indicate the air/gas flow rate and a needle valve for adjusting the flowrate.
Typical air/gas flowrates for bubblers are 8-30 cc/s (1 to 4 SCFH), a flow rate suitable to create a constant stream of bubbles from the dip tube.
The only 'calibration' of the pressure transmitter in a bubbler system is setting the range of the transmitter's 4-20mA output with a zero-to-span range that takes into account the maximum liquid column head pressure that the transmitter will 'see', which takes into account the specific gravity of the liquid.
Conversion to physical level units (accounting for specific gravity) is done in the receiver (indicator/PLC/DCS/PAC/controller).
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 2 No |
Hook up resistance decade box to temp.transmitter.
why pneumatic control signal output is use 0.2 to 1 kg/cm2
What is the procedure of DP switch calibration
what is PID n give me brief info. about P&I&D.
the basic of a DP flow transmitter are the following
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
what is wave length were using ?
What is the Difference between CNC and PLC
What is 1:1 redundancy ?
Dear Sir/Madam, I am attending an interview for ETs in BHEL. I have cleared my written test under Electronics (Instrumentation). This is the first time I am appearing for an interview. Can any one who has attended the interview earlier give me a clue to face the interview. With regards Sindhu
Please any one can explain how to calibrate transmitter (smart) online with out remove from the container suppose it is interface level or static pressure level measurement we dont want to remove transmitter from the container mean it is running plant please give me detail. thankx brothers
what is difference btween rotameter and orifice plate?