how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?
Answers were Sorted based on User's Feedback
Answer / komal
1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / ashwin jain
if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / haridass
1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.
2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / mr.georgemathews
It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.
The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.
This whole process will hardly take 5 min.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate temp.prapotional to mv in thermocoulpe.
what is the meaning of HART ?
Why do we need to install hook-up line differential pressure type level transmitter when the differential pressure type level transmitter with capillary are available?
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
Please send the all question with answer related for interview.
Calibration procedure for electro magnetic flow meter
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
what are turbo generators?
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
what is diff b/w neutron and ground?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)