Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?

Answers were Sorted based on User's Feedback



how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / komal

1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.

Is This Answer Correct ?    12 Yes 1 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / ashwin jain

if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.

Is This Answer Correct ?    7 Yes 4 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / haridass

1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.

2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.

Is This Answer Correct ?    3 Yes 1 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / mr.georgemathews

It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.

The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.

This whole process will hardly take 5 min.

Is This Answer Correct ?    0 Yes 0 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / ayaz

no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range 

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason

19 Answers   Ecoboard, Jindal, Sepco,


How can we cheak the ENCODER ?

1 Answers  


If the average power during generation is zero, why do the analog meters have + and - ?

1 Answers   Siemens,


If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?

5 Answers  


Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..

0 Answers  


what are the difference between conventional and smart transmitter.

1 Answers  


Explain what is meant by the term “FLASH POINT” of liquid?

2 Answers  


CAN WE CALIBRATE LEVEL TRANSMITTER USING HART COMMUNICATOR WHEN WATER LEVEL IS PRESENT IN THE BOILER SHELL?

4 Answers   Chemin, Emerson,


the output of the common trasmitter protocol in qatar gas are the following

0 Answers  


hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel

0 Answers  


WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?

8 Answers  


Coal mill Instruments Equipments for cement plant And process diagram ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)