Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?

Answers were Sorted based on User's Feedback



how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / komal

1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.

Is This Answer Correct ?    12 Yes 1 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / ashwin jain

if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.

Is This Answer Correct ?    7 Yes 4 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / haridass

1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.

2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.

Is This Answer Correct ?    3 Yes 1 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / mr.georgemathews

It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.

The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.

This whole process will hardly take 5 min.

Is This Answer Correct ?    0 Yes 0 No

how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp ..

Answer / ayaz

no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range 

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

how to calculate temp.prapotional to mv in thermocoulpe.

2 Answers   Electronics, KNPC,


what is the meaning of HART ?

2 Answers  


Why do we need to install hook-up line differential pressure type level transmitter when the differential pressure type level transmitter with capillary are available?

2 Answers  


PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear

0 Answers   MSL, SRAAC,


You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?

1 Answers  


when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?

1 Answers   UETCL Uganda Electricity Transmission Company Limited,


Please send the all question with answer related for interview.

1 Answers  


Calibration procedure for electro magnetic flow meter

0 Answers  


I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.

1 Answers  


what are turbo generators?

1 Answers  


WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??

2 Answers   IOCL,


what is diff b/w neutron and ground?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)