how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?
Answers were Sorted based on User's Feedback
Answer / komal
1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / ashwin jain
if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / haridass
1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.
2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / mr.georgemathews
It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.
The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.
This whole process will hardly take 5 min.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range
| Is This Answer Correct ? | 0 Yes | 0 No |
When cryogenic control valve will be applied?
Why humidity limit is 30 to 55 % for raw material storage?
which instrument is used to study the structure of phloem and xylem tissue?
IF PLC POWER FAILURE THEN WHAT HAPPEN?
is there any digitel grevity meter availaible in the market by which we can measure specific gravity of a battery?
which one is best profibus or RS485 for communication?
why we use 250 ohms across HART CALIBRATOR DURING CALIBRATION OF TRANSMITTER
Explain Split Range Control In Control Valve Briefly.
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
Vibration probe working principle?
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
What is the use of +/- 20ma in analog measurement,and which instrument gives +/-20ma output
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)