can i use capillary type dp transmitter converted to
capillary type pressure transmitter. if i removed one side
capillary tube its work correctly?
Answer / k.sreenivasan
To begin with you must ask why there was a DP measurement
in the first place?
For example if you are measuring the DP across a Filter to
find filter choked condition, then removing one capillary
will defeat the basic concept.
If the DP xmr is used for a level measurement, then also
you will get wrong reading.
So unless you inform the details... correct answer cannot
be given.
By keeping one side of the transmitter open to atmosphere
by removing one capillary, the other side will read the
pressure with reference to atmosphere.
If you want vacumm pressure measurement then you have to
keep the HP side open and LP to the process. Vice versa for
gauge pressure measurement.
Is This Answer Correct ? | 3 Yes | 1 No |
WHAT IS INSTRUMENTATION?
difference between span and range
Why Ma signal is using for control system?
What are primary elements of measuring pressure? Which type of pressure can be measured by these elements?
What is the right procedure for adjusting the gap voltage of bently nevada vibration sensor?
what is Micro-switch and where it is used......?
why we use condesiate parts before tranmitters?
what is difference between 3 wire and 4 wire RTD sensor?
12 Answers HTA Instrumentation,
what is difference between RTD , thermo couple and thermistor in general ?? (except temperature co-efficient )
Why DP transmitters are subjected to high static pressure test of 100 bar. Though they will be used for very small pressure range
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
what is relation between electronics&instrumentation